AC DC Ampere Rating

07/31/2008 7:30 AM

when the ac contator is using for dc current what will be the percetage of derating to be considedred

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: ac dc ampere rating

07/31/2008 10:12 AM

Follow the equipment manufacturer's ratings information.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#2

Re: AC DC Ampere Rating

07/31/2008 1:21 PM

This approximation uses the arching point -E.field strength- between the contacts.

Take the ac current as i = Ipeak.Cos(ω.t) then the charges those form the electrical field between contacts, will be

Qac = 2.∫i (from t=0 to T/4 seconds )

Qac = 2.(Ipeak / ω).|Sin(2∏/4) - 0| since ω = 2∏ / T then Qac = Ipeak coulomb.

Now assume that the dc supply is an unregulated voltage source as a rectifier output, then this charge will be

Qdcu = 2.(Ipeak / ω).2.|Sin(2∏/4) - 0| = 2.Ipeak clmb.

If the dc supply is a regulated - like an accumulator - then the above calculation yields:

Qdcr = ∏.Ipeak clmb.

Result: with a true dc current, the contact rating of the contactor decrease down to one third ( 1/∏) of that ac rating.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jul 2008
Posts: 93
#3

Re: AC DC Ampere Rating

07/31/2008 9:39 PM

I think the relay contact's rating depends also on the contact's voltage .

If you loock at the data sheet of Omron relay part # G5V-1-DC24 you find the contacts rating :

1A at 24 VDC

0.5A at 115 VAC

Where the contact DC current rating is twice the AC rating.

Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#4
In reply to #3

Re: AC DC Ampere Rating

08/01/2008 12:12 AM

Hello zacky ,

I think you are confused a bit.

1-It is essential to presume that the two systems are at the same power rating with thislike comparisons. I also do.

2- Please note that i used Ipeak for calculations, not Ieff.

Now let's play with your example, Omron's specs:

0,5A is the effective current. Ipeak = √2 .Ieff = √2 . 0,5 = 0,707 A ≈ 0,7A. (Our sample current is i= 0,7.Cos(ω.t) ).

Since voltage ratings are different we will compare "powers" not currents only.

1A at 24V yields 24W.

0,7A at 115V yields 80W.

24 / 80 = 1 / 3,33 ! This is even more what i said (1/∏). Omron also allocates a bit room for safety...

now okay?

regards

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: AC DC Ampere Rating

08/02/2008 9:20 AM

Seems overly complex. With the contacts closed equivalent RMS and DC current values will stress the contacts and conductors in the relay similarly ( P = I^2 * R). As the contacts open the current either peak or DC is only effecting the performance based on the inductance of the conductors and traces in the system. The stray inductance will try to keep the current flowing and can generate very high voltage arcs across the opening contacts. The system voltage also contributes to the arcing. But neglecting the stray inductance (because we do not know what it is) RMS and DC current will effect the contacts similarly. Assuming the inductance is figured in and the driving factor for current rating the DC level could be higher because the peak current for an RMS waveform would have to have been considered in the RMS rating. The only other thing I see is the RMS waveform will create an sinusoidal (sine wave current assumed) heat profile on the contacts and conductors with an average heating effect equal to the DC heating effect, but it will have peak temperatures higher than the constant DC heating effect.

I am not a relay guy but that is pretty basic analysis. Please correct me if I am missing something

Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#6
In reply to #5

Re: AC DC Ampere Rating

08/02/2008 11:55 AM

Hello Guest, thanks for your reply.

I will try to clear my way of solution (#2).

1- Cause of using Ipeak instead of Ieff is just getting rid of (√2) crowd in equations. This is no effect on results. If u want to use Ieff then multiply the currents of ac with a √2, that's all.

2- The kind of load - resistive or inductive- also not important for this comparison. Of course with an inductive load it would be important the self emk effect of inductances and I^2*R thermal effects on contacts. But whatever the conditions are, those will be valid both AC and DC.

Think of a loaded contactor is just opening his contacts. Voltages are voltages and currents are currents. How to differentiate the AC and DC?

This is why i have used an approximation concerning waveform of the energy and have got into account the available charges those will ionize the media. The effect of stray inductances - but load inductance! - could be neglected relative to this ionizing field.

This is not a complete analyzing of arching with a specific circuit, this is only a comparison between ac and dc, under the same power and environmental conditions.

Isn't this what the S. Murali is asking for?

Best regards

Register to Reply
Anonymous Poster
#7
In reply to #6

Re: AC DC Ampere Rating

08/02/2008 2:16 PM

For the example of the Omron relay mentioned above , how come the relay contacts depen on the voltage ( 24V or 110V) while the contacts voltage is zero when the contacts are closed.

Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#8
In reply to #7

Re: AC DC Ampere Rating

08/02/2008 4:49 PM

Dear Guest, i'm surprized with this question..

As long as the contacts are closed the i2*R dissipation is in action. This is no matter provided that the actual current is not bigger than what the spec say.

Arching phenomenon will be question while you just open these contacts!

okay?

Register to Reply
Register to Reply 8 comments