wire gauge by inspection

08/04/2008 5:09 PM

Trying to identify wire gage of stranded power cable. Each stranded conductor has seven solid wires of #10 Ga copper. Power cable itself is flexible and stranded. Consist of 3 power conductors inside an armored jacket.

My B&S wire gage will fit over the stranded bundle as a #1 Ga but not a #2 ga. But that does not account for the voids between strands in the bundle. Cable is already installed and the portions I can access does not show any printing or identification. Is this actually a #2 Ga power conductor for purposes of determining ampacity. So far I have not found an online catalog giving cable construction details such as stranding, gage of this stranding and equivalent total Ga for ampacity rating.

__________________
Elnav
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Location: OH USA
Posts: 549
Good Answers: 27
#1

Re: wire gauge by inspection

08/05/2008 10:42 AM

The 7 strand conductor you describe is close to #1 AWG Class A stranding (although it consists of 7 strands of 0.1093" wire whereas #10 AWG is 0.1019" diameter). The overall diameter of #1 Class A is 0.328" whereas yours would be 0.306".

If all that is correct, you could safely derate the ampacity of jacketed #1 AWG Class A (under the same operating conditions) by 7%.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#2
In reply to #1

Re: wire gauge by inspection

08/05/2008 11:40 PM

Thanks! My stranding consist of 0.099" X 7 and the bundle measures 0.305" - 0.302" depending on which set of strands I measure across. If I treat the bundled six solids like a "hex" nut; the measure across flats is 0.283" and across the point is 0.305 largest set. Slight variance due to cutter squeezing the bundle.

Looks like I had better derate it by 7% from a #1 AWG Class A to be on the safe side. The strands are coated with a nylon film and the cable is constructed like a direct burial TEK cable, even though it is installed above ground.

__________________
Elnav
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#3

Re: wire gauge by inspection

08/06/2008 6:42 AM

You need to find the circular mil sum of all the strands in the conductor and then determine the equivalent AWG wire size from a AWG table.

Use a micrometer or your wire gage to measure a single strand.

Calculate or look up (in the AWG table) the equivelent circular mill cross sectional area for this single strand.

Multiply this value by the number of strands. This gives you the total cross sectional are of all the strands.

Go back to your AWG table and convert the cross sectional area back to equivalent AWG wire size.

Snakers

Register to Reply
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#4
In reply to #3

Re: wire gauge by inspection

08/06/2008 12:16 PM

Yes I realize that I need to find the equivalent AWG by summing the circular mills of the individual strands. I am using a micrometer as well as a Brown and Sharpe wire gauge.

The question arose because I arrived at an answer that appeared to be in between a #2 and a #1 wire. Maybe the wires were over drawn so they are slightly thinner than what they wer supposed to be. One thousands of an inch in 100 ( 0.100") is 1% error. Is that an allowed tolerance when drawing copper wire?

To be on the safe side I will use fusing based on the cable being a #2 rather than assuming it is #1.

Thanks to all for the replies.

__________________
Elnav
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bluestone (1); elnav (2); Snakers (1)

Previous in Forum: CBS   Next in Forum: Microwave-IR thermometer
You might be interested in: Gage Blocks, Cable Laying Services, Cable Assemblies

Advertisement