08/06/2008 4:40 AM

I carried out a test on a contactor to know the release and operating voltages for both DC and AC power supplies. I first used a varriable AC voltage 0-220v, the contactor coil was energised at 158v and later i gradually reduced the voltage untill it de-energised at around 120v. Then i replaced AC with a varriable DC source with 0-220V, the operating voltage was 53v and the release voltage was 12v. The gradual increase in AC caused the contactor hamming but for DC there was no any hamm and it was silent,so my question is what causes that differance in the release and operating voltages for the two power supplies.

thanks.

__________________
poy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Jul 2007
Posts: 4448
Good Answers: 143
#1

Re: Differance in DC and AC operating and release voltages for an AC Contactor

08/06/2008 5:46 AM

Because you have some force trying to open the contactor (a spring or gravity), whenever the magnetization approaches zero, the contactor begins to open. With ac, the current goes through zero twice per cycle and, at each zero crossing, the contactor begins to release. This is the hum or chatter you hear. DC does not go through zero and, therefore does not hum.

Now, look at a typical iron core hysteresis curve

http://www.ndt-ed.org/EducationResources/CommunityCollege/MagParticle/Physics/HysteresisLoop.htm

you see that some residual magnetization remains when all magnetizing force (proportional to current) is removed.

If the ac current is high enough, there will be enough residual magnetization to hold the contactor closed till the next cycle. Thus, at high voltages, the ac coil does not hum. This is not a good idea usually since the current is often high enough to overheat the coil. A small "shorting ring" can be added to the coil to provide slightly out of phase magnetization which will be enough to hold the contactor during the zero crossing.

In a dc coil, the residual magnetization may be enough that the contactor will not release quickly, and a small air gap is often included in the magnetic circuit to minimize this effect.

So, in general, a dc contactor should not be used on ac and vice-versa.

__________________
"Well, I've wrestled with reality for 35 years, Doctor, and I'm happy to state I finally won out over it." Elwood P. Dowd
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2008
Posts: 927
Good Answers: 56
#3
In reply to #1

Re: DiffAre: Differencend AC operating and release voltages for an AC Contactor

08/07/2008 12:43 AM

TFP45's reply is perfect!

Back in the 80's I used to do a pre-inspection of experimental aircraft prior to the FAA examiner showing up. The use of AC rated switches in DC circuits was verboten in my opinion and when I saw them insisted that they be changed for properly rated switches. The frequency with which this occurred prompted me to write an article that was published in 1986. It still can be read at:

http://www.eaa.org/sportaviation/2005/0502_switches.pdf

The rate at which a DC switch opens is as vital to its survival as any other factor I know. DC contacts have to be separated FAST!

Those that open slowly, are typically AC rated and, as TFP45 wrote, depend heavily on the transition period, when alternating current is not flowing.

L. J.

__________________
"Both the revolutionary and the creative individual are perpetual juveniles. The revolutionary does not grow up because he cannot grow, while the creative individual cannot grow up because he keeps growing." Eric Hoffer
Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#4
In reply to #1

Re: Differance in DC and AC operating and release voltages for an AC Contactor

08/11/2008 6:11 AM

Thanks alot gents, now i have the full info on that.Thank you

__________________
poy
Register to Reply
Power-User

Join Date: Jun 2008
Location: TR
Posts: 142
Good Answers: 1
#2

Re: Differance in DC and AC operating and release voltages for an AC Contactor

08/06/2008 11:06 PM
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

feridun (1); Laughing Jaguar (1); olivinak (1); TVP45 (1)

Previous in Forum: Heating Load   Next in Forum: discovering torque values - - transducers

Advertisement