Loud Bang When Air-Break Switch Was Opened

08/11/2008 11:20 AM

Anyone with a crew here?

Two three phase 10000KVA 66kv/11kv stat-delta transformers were in parallel at a substation,their primaries are connected to 66kv transmission line through a single airbreak switch designed to interupt magnitizing current only,which is less than 1amp. The transformers were being removed from service and the secondary loads had been removed.The technician started to open the air break switch with an idear that he will see a small arc as he was interupting the magnetizing current,but he was suprised to here a loud bang and a ball of frame where the air break switch contact had vapourised. What could have gone wrong?

__________________
poy
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Jul 2008
Location: Finland
Posts: 22
#1

Re: Loudbang when Air break switch was opened

08/11/2008 2:20 PM

You don't give much information about those two transformers. Are they identical or one installed later than the other one? One possible explanation is circulation current between these two transformers due to the different short circuit impedance, bus impedance and the difference between transformer secondary voltages... These currents exists even when transformer operate parallel in no-load conditions.

Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2008
Posts: 50
#2

Re: Loud Bang When Air-Break Switch Was Opened

08/12/2008 1:01 AM

Dear Sir,

The phenomenon of hearing " A loud bang with a thick ball of flame ", this only happens when the electrical load is not isolated 100%.

Especially when we operate any breaker, we should also check varify whether all the 3 phases are physically isolated otherwise there may take place inevitable mishap.

In elctrical circuit we should make 100% sure that the equipment is 100% isolated from both the sides of the electrical load just to avoid possibility of any electrical hazard to the existing power system. Also both sides of the circuit breaker under maintenance should be properly earthed .

Regards,

Ulhas Pradhan

Register to Reply
Anonymous Poster
#3

Re: Loud Bang When Air-Break Switch Was Opened

08/12/2008 1:10 PM

Blowed up Sir.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Heilonjang China. 2 blocks from you
Posts: 109
Good Answers: 5
#4
In reply to #3

Re: Loud Bang When Air-Break Switch Was Opened

08/28/2008 10:53 AM

Yes its all about circulating currents because an air break is to interupt the magnetising currents just as the isolator dose inturupt the line charging currents.

upon closer inspection it was reavealed that the two transformers had been set on widely different taps.These transformers had 7 percent impedance. Because the turns ratios were unequal a circulating current was set up even if the secondary loads were removed.The current through the air break switch supplies the reactive losses of both transformers and therefore lags the primary voltage by 90 degrees.The resulting current can exceed the interupting rating of the switch, causing it to fail.

__________________
poy
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Flux (1); olivinak (1); umpradhan (1)

Previous in Forum: Monitored Generator Parameters   Next in Forum: Your Hard Worked Design Taken Away From You?

Advertisement