- What is the best method/instrument for underground fault detection
- is there a good web site explaining the most popular methods
- Is there a set of calculation or rule of thumb to use for the voltage and current magnitude on a thumping method. Let us say the voltage is 15 kv rated on 3 phase 13.8kv system, cable length 5,000m.
- what is the best method to detect the fault on open neutral, and also for low voltage 600, 208, 3 phase underground cable fault
- is there different methods to be used for cables with uninsulated grounding cables
Re: underground fault detection
08/15/2008 3:18 AM
<...What is the best method/instrument for underground fault detection...>
Mk.1 eyeball. Look for a huge crater. The fault is there somewhere.
Good Answers: 42
08/15/2008 10:51 AM
The best and fast method of locating Under ground cable fault is to trace the fault with the help of a cable fault locater. I am using an APLAB make ( Manufactured by M/S APLAB India Pune) cable fault detector and the instrument pinpoints the fault location. I am fully satisfied with their instruments. Visit the following link to see the various models manufactured by them.
http://www.aplab.com/cfl/cfl02.htm
08/18/2008 5:44 PM
A thumper works best for underground electrical cables. Communications faults can be precisely located with a TDR (time domain reflectometer)