how to calculate the range of relay used for star delta starter for an example moter rating is 30 kw
Good Answers: 19
Re: range of relay
08/15/2008 1:01 PM
Let us assume the following:
Motor rating 30 kW
Efficiency 100 %
Power factor=0.8
applied Voltage=415 V (L-L)
The full load Line current would be(Iline) =(30*1000)/(415*0.8*1.732)=52 .17 Amps
The phase current would be(Iphase) =Iline/1.732=30.1 Amps
In a standard Star Delta starter the thermal over load relay would be in Delta formation, therefore the over load relay range should 21-36 amps.You can set the range from 70 % to 120 %
Ramesh,Freelance Electrical/automation Consultant
Re: range of relay
08/16/2008 5:01 PM
thanks for giving logical answer
Re: range of relay
02/15/2011 6:30 AM
what to be the relay amps to be set for idial condition
Good Answers: 804
Re: range of relay
08/15/2008 1:18 PM
Or just take the shortcut, especially since you failed to provide details on the motor other than the kW rating.
Read the motor nameplate, multiply the FLC x .58