Ground Cable

08/19/2008 10:33 AM

Gentlmen,

Is the insulataion of ground cable "green color" same like for line cabes, I mean can I use it in the feeders of 1 MW transformer?

The cable size is 70mm

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jun 2008
Posts: 1
#1

Re: Ground Cable

08/19/2008 10:42 AM

The cable should have its insulation value imprinted on the insulation itself. You may confirm voltage and current capabilities relative to the type of insulation on the cable. Green should not be used as a feeder cable.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Ground Cable

08/19/2008 11:06 PM

Generally No (certainly no if you are planning to use it on the high voltage feeders, eg- 1kV and above). Check your cable specifications for rated voltage ratings.

I am assuming you are NOT planning to use "green" coloured earth wire as a phase conductor (which is illegal in every country I can think of).

Consult your local electrical standards and/or cable manufacturer for more information.

__________________
jack of all trades
Register to Reply
Participant

Join Date: Aug 2008
Posts: 2
#3

Re: Ground Cable

08/19/2008 11:18 PM

It depends on the cable insulated material use, is this cable insulation's material PVC insulated , or is it XLPE insulated. Is it armoured as well. It will be fine if the material is XLPE material, however, when colour code is in concern, it might not be acceptable to be put to transformer use, unless it is use for grounding all the metal body parts of the transformer.

Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#4

Re: Ground Cable

08/19/2008 11:29 PM

Like they said no. The insulation on the grounding wire is cheaper and biodegradeable usually.

__________________
If you never do anything you never have problems.
Register to Reply
Power-User

Join Date: Nov 2006
Location: antwerp/belgium/europe
Posts: 160
Good Answers: 5
#5

Re: Ground Cable

08/20/2008 1:34 AM

In many countries (at least in ALL countries in the EU) ground cables HAVE to be green and yellow.
Green or yellow cables are absolutely forbidden for any purpose. (Except inside appliances and less then 50 Volts)

__________________
44mEurope
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#6

Re: Ground Cable

08/20/2008 3:23 PM

i wont advise it...as it always going to confuse you.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Register to Reply 6 comments
Copy to Clipboard

Users who posted comments:

44mEurope (1); chaterpilar (1); cokoh2 (1); dadw5boys (1); gare (1); jack of all trades (1)

Previous in Forum: Equipment Cooling and Humidity Challenge   Next in Forum: Earthing Transformer vs. Transformer Reactor
You might be interested in: Stock and Strip Feeders, Solids Feeders, Parts Feeders

Advertisement