Imagine a system of closed equipment cases where each case (about 3 cubic feet in volume) includes a 5000 BTU evaporator (Part of a R134 cooling system) and a 450 CFM fan on one end. There is some control via a thermal expansion valve in the refrigerant line. The case is ducted such that air flows from end A to end B around the outside of the equipment and returns through the equipment (B to A) across such evaporator coil. Now imagine the other end having an access lid where this lid is frequently removed for equipment front panel access in a hot and humid environment.
When the system is sealed (nearly air tight), there is negligible condensation and equipment operating temperatures are well within their specified ranges. With the lid off, such a system acts very much like a de-humidifier causing substantial condensation (yes a drain is present; preference is not to have condensation on or near electronic equipment). This condensation coupled with airborne contaminents is believed to be the culprit for some electronic anomolies.
What approaches can anyone recommend to mitigate the "de-humidification process" (collection of water in the case) while accessing the front panel in a hot humid environment?
T
Good Answers: 18
Re: Equipment cooling and humidity challenge
08/19/2008 9:49 AM
Oddly enough, I have been confronted with much the same problem, and it ain't as simple to solve as one may think.
Among other ideas, one that made the most sense was to build a room around the equipment cabinets, the enviroment of which was to be well conditioned, and we actually did that in one computer server equipment room recently (super-conditioned space within an air conditioned space), but not in the original case I mentioned earlier.
The solution we eventually arrived at, with a keen eye on cheapness, was to suck air out of the equipment cabinets with high pressure fans (typically used to cool electronic equipment) so that invasive, humid air could not enter the cabinets. Over time, the very slight vacuum we created by doing that eventually stabilized, but by then, the internal air conditioning system returned things to normal without much condensation at all.
08/20/2008 8:37 AM
Can you provide more information about this "high pressure fans" approach? In my application, I envision a relatively large volume vacuum pump attached to my case with say a 2 inch air duct. When I remove the lid, conduct front panel operations and re close, I would then activate this pump for some 5 to 10 minutes to evacuate the case. Am I on the right track?
Good Answers: 38
Re: Equipment Cooling and Humidity Challenge
08/19/2008 12:54 PM
Depends upon what is accessed during the opening of the lid. If all you are doing is taking information from readouts or pressing buttons, how about using a membrane to seal off the electronics from the outside air and still allow you to read or press buttons through the membrane?
Just a thought!
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
08/20/2008 8:25 AM
A membrane is an excellent idea. Part of this challenge (I did not mention) is the need to insert and remove raid drives from servers. Since this drive movement operation is done on the order of once a day, perhaps the membrane could be somehow made like a rubbermaid lid for the case; peel back membrane insert drive-reseal membrane?.
Good Answers: 266
08/19/2008 4:47 PM
Auxilary Vortex tube cooling to place positive air flow at panel opening.
United States - Member - Old Member
08/20/2008 9:43 AM
Have you tried the air curtain approach? Forcing the air accross the opening will create a resistance & seperate the ambient from the interior or the case. Case in point, your supermarket freezer case. You would have to play with air flow & C.F.M."s (different motors & fan blades).
Good Answers: 38
08/22/2008 2:06 PM
Okay here goes nuthin. Install drive bays where all you have to do is unlatch the lock mechanism and the drive slides right out. This way there is no need to access the backside of the drive to unplug the power and IDE cable. Place seals around the front of the drives to minimize moisture getting in. Place the moisture membrane back in place and start the cooling units. This should remove any condensate in the bay. After a few minutes start the units up.