How to properly calculate the " Consumed KW Load "
Please confirm or correct the following :
Non - Motor Loads assume PF = 0.98
IEC Motor Loads ? ( Help )
IEC Motor gives the Shaft Power in KW at the nameplate Efficiency ?
e.g. Nameplate : 3 phase, 10 KW motor, fla = ? ( KW / ( KV x 1.732 x pf ) ?
PF = 0.70, Efficiency = 0.85 or fla = ( KW x I.732 x pf x efficiency ) ?
Load Factor given as 0.75.
What is the Power by the Motor ?
10 KW x 0.75 LF = 7.5 KW
I do not see Efficiency required to calculate the Consumed Power ?
Input Power is rated for 10 KW ? and not 10 KW / Efficiency ?
Efficiency to me is the Electrical Power Output to the Mechanical Load.
and that is ( 10 KW x Efficiency )
What is the IEC defination of " Absorbed KW " as it would relate to Consumed Power ?
I assume that the Motor Full Load Amps is derived from the 10 KW ?
Thank you