08/27/2008 2:10 AM

The Power supply INPUT drawn by an electrical motor under load conditions is determined by the power KW required to drive the connected mechanical load under normal operating load conditions.

The Mechanical Load Factor = Mechanical Load KW / Motor Shaft rated output KW

Consumed Power KW = [ Power Input KW / Motor Efficiency ] X Load Factor

Is this correct ?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Consumed Power / Load Study

08/27/2008 2:41 AM

Hello Jeff Millar

Basically: Yes.

There are other small losses (bearing noise, heat, rotor windage, fan losses etc) but these all come under the basic heading of Efficiency.

Do not forget the Electrical Power Factor of the motor, at variable loads and speeds. If the motor is large, an automatic Power Factor Correction unit may be used to minimise losses.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Anonymous Poster
#2

Re: Consumed Power / Load Study

08/28/2008 9:27 AM

Introducing an alternative:

pump motor is calculated using the following formula:

P=γ Q h/ ŋ 3600

Where:

- P will be computed in W;

- γ is specific weight in N/m³;

- Q is pump flow capacity in m³/h;

- H is discharge height in m;

- ŋ is the motor-pump system total efficiency factor ( 0.50÷0.70 )

Register to Reply
Power-User
Engineering Fields - Mechanical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: May 2007
Location: Parallel 45
Posts: 226
Good Answers: 21
#3

Re: Consumed Power / Load Study

08/28/2008 9:34 AM
Introducing an alternative in particular ( sorry before I posted the reply as a guest):

pump motor is calculated using the following formula:

P=γ Q h/ ŋ 3600

Where:

- P will be computed in W;

- γ is specific weight in N/m³;

- Q is pump flow capacity in m³/h;

- H is discharge height in m;

- ŋ is the motor-pump system total efficiency factor ( 0.50÷0.70 )

__________________
Look over to the next challenge
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4

Re: Consumed Power / Load Study

08/28/2008 11:57 AM

Your first sentence is correct but the 2nd formula is wrong.

Consumed electrical power kW = power input kW = power output kW / motor efficiency = mechanical load kW / motor efficiency.

One thing you need to watch is that motor efficiency varies somewhat with load (actual power output). Motor data sheets usually give efficiency at 100%, 75% and 50% of rated power output.

Cheers........Codey

__________________