Anonymous Poster

heat transfer

08/27/2008 10:20 PM

hi, i have installed d/p flow transmitter on the steam line. i run leads from root valve to the transmitter about 6 meter, leads filled with demin water, i just want to know how much temperature will travel up to the transmitter?

steam temp. 300 deg C

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2008
Location: Mumbai
Posts: 250
Good Answers: 2
#1

Re: heat transfer

08/28/2008 12:47 AM

Hi,

I suppose you have to use Condensate pot For steam Application as per std Installation Details

Regards

Jose

Reply
Anonymous Poster
#2
In reply to #1

Re: heat transfer

08/28/2008 3:44 AM

Hi, the installation of the transmitter is with condensate pot, mounted on the process root valve, i huw much heat will transfer to the instrument manifold or every 1 foot how much temp? will travel toward manifold.

Reply
Associate

Join Date: Jun 2008
Location: Houston
Posts: 30
#3
In reply to #2

Re: heat transfer

08/28/2008 10:53 AM

You would loose about 100 deg per foot. This was the rule of thumb for designs in the EPC firms when working with High Temp applications such as steam and super heated steam applications. the other consideration is always make sure to mount to the side or below the Heat source. If you are using filled lines mounting below will always help in keeping the impulse lines filled. Otherwise one has to calculate the tranference of temperuature overtime through the buffer media that will have a heat coefficient.... Hope this helps.

Reply Score 1 for Good Answer
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); josej (1); ral412 (1)

Previous in Forum: Flow measurement using orifice plate   Next in Forum: callibration procedures of callibration of temperature transmitter

Advertisement