Anonymous Poster

current carrying capability

08/30/2008 4:03 AM

From Coductivity & Dimension of a Aluminium Bus bar can we calculate the max Current carrying capability of tht bus bar?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#1

Re: current carrying capability

08/30/2008 10:11 AM

yes

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Reply Score 1 for Off Topic
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: current carrying capability

08/30/2008 12:25 PM

Shawn: short and straight to the point.

answer is here : http://www.electricianmath.com/neccalculations/busbarampacity.htm

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#3

Re: current carrying capability

08/31/2008 2:37 PM

The current capacity of Aluminum conductor is 710Amp./1square inch of conductor area.@ room temp. (20°C). This number is de-rated as temperature is increasing. Max allowable conductor temp. as per the NEC, for continues operation in free air is 50°C. If at rated capacity (for lack of ventilation for example,) temp. rise is over the max permitted, than next size conductor must be used. The conductivity is already taken into account in this number.

Hope it helps

Wangito.

__________________
Never trade luck for skill.
Reply
Anonymous Poster
#4
In reply to #3

Re: current carrying capability

09/02/2008 2:05 AM

Hi,

But the normal ambient temperature considerd being 50 deg. C.

Regards,

N.Suresh

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#6
In reply to #4

Re: current carrying capability

09/02/2008 10:25 AM

If 50°C is your ambient, and without too much calculations, from the tip of my head I would say double the bus-bar size. (i.e 300A/inch2) avoiding sharp turns and watching for possible bi-metal reactions between your fastening hardware and the Al bus-bar.

Why use Al anyhow? I hate Al as a bus-bar material...

Wangito.

__________________
Never trade luck for skill.
Reply
Anonymous Poster
#5

Re: current carrying capability

09/02/2008 8:47 AM

IEEE std 605 gives long and very detailed instructions on calculating the ampacity of bus bars at differing temperatures and geometries. It even goes into support spacing and the effect on SC withstand. Covers Al and Cu...

Reply