CT

08/31/2008 8:01 PM

Which factor is determining Knee volt for a CT? for a multi core CT, whether the Knee volt is high for higher trun secondary core or lower turn secondary core?

__________________
?????????? ????????? ????????,.........??????? ???????????? ???????? ????. ????????????
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#1

Re: CT

09/01/2008 9:27 AM

The knee volt in a ct is where the CT windings saturate.. The test can be performed with a voltage supply (0-250V) with rheostat, and a multimeter placed in series with one of the leads and set to amps.

Connect you power supply to x1 & x2 of CT and begin injecting voltage in steps of ten volts, while documenting current reading. The point in where the current reading becomes non-linear is your knee point.

The CT should be labeled C50, C100, C200, etc.. Those numbers reflect where your kneepoint should be in test..

The kneepoint reflects the amount of voltage the CT will be able to produce at 20 times normal current. If the CT is not sized properly it will saturate under fault causing protective relay to not see current therefore not operating.

As far as multicore (tap) CT I do not believe the tap setting will effect kneepoint, but am not 100% positive. Perform saturation test at all taps and you will know for sure..

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: CT

09/01/2008 10:28 AM

1- CT's knee point voltage relate to it's rated volt-ampere, rated secondary current, rated secondary resistance and rated accuracy limit factor.

Uk=ACF x ( VA/In+Rct x In )

2- In multi secondary winding (tap) current transformers (please don't say multi core) higher knee point voltage is related to higher tap.

--------------------------------------

Creative thinking is enjoyable, Then think about your surrounding things and other thought products.