Motor Rating

09/01/2008 12:59 AM

In an electrical network some motors are mentioned in MVA rating, say example one MVA, 15% imp. What it means. Actually, motor loads are mentioned in kw Or hp. why here is mentioned in MVA? Please clarify it.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Motor Rating

09/01/2008 3:24 PM

Motor rating usually expressed in KW or HP as engraved in the motor name plate, but large motors rated at medium voltages can rather be expressed in per unit values for the purpose of load flow analysis eg. KVA/MVA in addition to the % impedance of such motors to analyse the load flow in the network.

The correspoding KW rating is equal to the KVA rating multiplied by the power factor of the motor as identified by the motor manufacturer.

P = S*P.F

where S= apparent power expressed in KVA.

P = active power in KW.

P.F = power factor

Reply Score 1 for Good Answer
Associate

Join Date: Aug 2008
Posts: 39
#2
In reply to #1

Re: Motor Rating

09/02/2008 1:43 AM

Thank you sir.

Reply Score 1 for Off Topic
Reply to Forum Thread 2 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!

Previous in Forum: pf in 3-phase.   Next in Forum: Low oil level of power transformer

Advertisement