Low oil level of power transformer

09/01/2008 1:54 AM

Dear all,

We have 8 power transformer with spec : 13.8kV/115kV, 28MVA, cooling system OA/FA1/FA1. Date macnufactured 1996 That transformer use nytrogen fill in the tank. Base on our inspection by infra red camera we found 6 transformers were low oil level. Our crew have made sure that all radiator's valve were opened.

Could you please explain to us what root caused probably.

Thanks in advance,

Kuncoro

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Mar 2008
Location: South Texas - SOMETIMES
Posts: 88
Good Answers: 4
#1

Re: Low oil level of power transformer

09/01/2008 8:55 AM

Are the transformers showing low oil level loaded the same as the one showing normal oil level?

What does your level guage show?

If your transformers do indeed have low oil level, it can only mean they were not filled properly from installation, or you have a leak in a bushing, valve, etc..

The transformers must be loaded equally if possible to allow better comparison of IR images.

Register to Reply
Associate

Join Date: Aug 2008
Posts: 31
#2
In reply to #1

Re: Low oil level of power transformer

09/01/2008 6:41 PM

Hi ekiechle,

Yes, all transformer were showing low oil level. And we thought oil level were on normal level. We have made sure too those radiator's valve already opened.

Level guage doesn't show low oil level. No bushing leakage.

Our crew will add some oil transformer

Should you have any comment please advice

Thanks,

Kuncoro

Register to Reply
Anonymous Poster
#3

Re: Low oil level of power transformer

09/02/2008 1:24 AM

Hi,

The Oil level gauge (MOG) and the Prism level gauge will give the level oil in the transformer. Any Leakge might have been noticed visually in the Transformer. Low level Oil will activate the alarm also. Thsi also can be identified from the RTCC Panels facia. I don't the understand the requirement for IR camer as all lekages can be visually identified.

If you want to identify the the loaction of lekage then take shut down of the transformer apply soap solution over and identify the where bubble occurs which is the leakage point. This most simpler and effective method.

After identification as a temprory measure apply sealing compound.Call Factory's manufacturing Engineer to do bracing on the lekage point.

Regards,

N.Suresh

Register to Reply
Associate

Join Date: Aug 2008
Posts: 31
#4
In reply to #3

Re: Low oil level of power transformer

09/02/2008 1:38 AM

Hi Suresh,

Thank you for your response, clear understood

Register to Reply