I had come across a motor which is used for ATT ( Automatic turbine trip ) in NTPC power plants, supplied from germany has the name plate of,
230/400 V, 0.18 KW, 50 HZ, 1.15/0.67 A , Star/ Delta, 0.73 pf.
But these values are talling in power equations.
Good Answers: 230
Re: motor
09/01/2008 9:01 PM
Hello k.dhana
Are you making a statement?
are you asking a Question?
Your Topic is not explaining whether you want an answer or a discussion.
What is "talling" ?
Reply here, with
Kind Regards....
Re: motor
09/01/2008 10:36 PM
That is standard information for a motor. What were you expecting?
Re: motor
09/02/2008 11:25 PM
This means motor rating is 0.18kw, if connected in star amps is 1.15 and in delta 0.67 and pf is 0.73.The motor can be connected in star or delta .For Any more info u need to clarify what u need
Good Answers: 804
Re: motor
09/03/2008 3:23 PM
I you are asking what it means (I'm not clear on what you want either), then it means that if you connect it to a 230V supply, you will connect the motor according to the Delta pattern and the current will be 1.15A at full load. If you connect it to a 400V supply, you will use the Star pattern and it will draw 0.67A at full load. Either way, the power factor is 0.73 and the output shaft power rating is 0.18kW (180W).