Previous in Forum: sandwich pam el shelters   Next in Forum: carbon steel
Close
Close
Close
5 comments
Rate Comments: Nested
Anonymous Poster

air conditioning question

09/02/2008 2:36 PM

how to find out the tonnage of fan coil unit or air handling unit,whether it has been fixed with the chilled water system or it has been kept inside the store ,what will be the formula or the method to find out the tonnage of in both ways,let me know,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Manufacturing Engineering - New Member Hobbies - Target Shooting - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Dec 2006
Location: Charlotte, NC USA
Posts: 791
Good Answers: 17
#1

Re: air conditioning question

09/02/2008 5:13 PM

Your question has so many parts I don't know where to start. First you can't measure the surface area of a the coil to determine the tonnage. The tonnage is determined as much by the size of the compressor as the size of the coil. Your best bet is to look at the name plate, the tonnage is there altho in code, but it is there.

If your asking about what tonnage you need for a given size room or building, then you need to do a load calculation, many are available on the web. just goggle it.

__________________
Be careful of what you wish for .....
Reply
Anonymous Poster
#2
In reply to #1

Re: air conditioning question

09/02/2008 9:37 PM

someone had told me about the calculation of tonnage of AHU through GPM and delta T, but i want to make sure of it,plz reply

Reply
Anonymous Poster
#3
In reply to #2

Re: air conditioning question

09/02/2008 10:01 PM

The formula Q [Btu/hr] = 500 x GPM x ΔT is for chilled water through chillers or coils.

Where 1 Ton = 12000 Btu/hr

EXAMPLE:

Size chilled water flowrate for 40ton chiller

Q=500 x GPM x ΔT

(40 ton)(12,000 BTU/Hr)=500 x GPM x (54 - 44 Deg. F)

GPM = 96


Is that what you are looking for?

Reply
Anonymous Poster
#4
In reply to #3

Re: air conditioning question

09/02/2008 10:26 PM

yes , im looking for this butcould u tell me if yhe air handling unit is kept in the open yard and if u want to calculate the tonnage of it,how we can do that,coz the tonnage is not mentioned on the name plate only the kw or the model num and moror capacity, plz let me know

Reply
Anonymous Poster
#5
In reply to #4

Re: air conditioning question

09/03/2008 10:22 PM

plz tell me the formula for calculation of CFM and LTS (litres per sec)airflow from FCU or AHU

Reply
Reply to Forum Thread 5 comments

Previous in Forum: sandwich pam el shelters   Next in Forum: carbon steel