Control Valve Station Piping

09/02/2008 7:03 PM

While not really an instrument question, I am not just a "balloon" guy.

I have seen many corporate and industry standards regarding control valve/bypass stations. Some have reducers before the station (typically control valves end up being one size below line size) and some after the block valves. Obviously this affects the pricing of the block valves, particularly in alloy piping. What are the cons, in your experience, by reducing before the control valve/bypass station, reducing block valve size to save $?

Register to Reply
Pathfinder Tags: control valve stations piping
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Control Valve Station Piping

09/04/2008 9:15 AM

yes. Economics

Register to Reply Off Topic (Score 5)
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#2

Re: Control Valve Station Piping

09/04/2008 9:24 AM

I would install a reducer at the inlet and outlet to the regulator. The one-size smaller regulator usually has more than enough capacity to serve the downstream piping. Any other reduction in valves or piping would not be wise, because of excessive pressure drop, either now or in the future. Hope this helps.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2008
Posts: 16
#3

Re: Control Valve Station Piping

09/04/2008 2:15 PM

In general, the block valves are installed at full line size. the only reason why the reducers are installed around the valve, is so that the desired min and max flow rates at predetermined pressure drops are controllable by the control valve. usually the pressures are fixed by the material handling process and magically, the control valve must be selected as such to satify everyone.

the line is sized as according to the design criteria, current capacity and future requirements. so, you could have more than one reducer upstream of the control valve. but the block valves should be procured and installed as according to the line size and not to follow the control valve sizes.

Register to Reply
Guru
Engineering Fields - Piping Design Engineering - New Member Egypt - Member - Member since 02/18/2007

Join Date: Feb 2007
Location: Cairo, Egypt
Posts: 1733
Good Answers: 248
#4

Re: Control Valve Station Piping

09/05/2008 2:41 AM

For this reason, I recommend to use ISA Recommended Practice for selecting size of control valve and all dimensions of piping controlling circuits to adapt with your piping layout.

The Recommended Practice ISA RP75.06 for Control Valve Manifold Designs, printed in USA by the Instrument Society of America, ISBN 0-87664-656-9.

This Recommended Practice ISA RP75.06 includes 6 Tables and 6 Figures showing type of control valve manifold dimensions for ASME class 300.

__________________
It is better to be defeated on principles, than to win on lies!
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Abdel Halim Galala (1); Anonymous Poster (1); flyinghigh (1); khangnguyenca (1)

Previous in Forum: Etymology of the Days of the Week   Next in Forum: dipsticks
You might be interested in: Gas Valves, Industrial Valves, Solenoid Valves

Advertisement