System: 220/33 KV TRX has stepping down by another TRX of 33/11 KV

Problem: Due to single phasing (blowing off fuse) of 11 KV load side, I/C Breaker of 220 KV side being tripped.

What could be the reason?

__________________
manirul
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: Tripping of Incomer Breaker

09/03/2008 5:51 AM

Hello manirul

The fault which caused the blown 11kV fuse on the load side of the transformer, is reflected magnetically through the transformer, and caused the primary (220kV) breaker to trip.

This is a normal condition, depending on setting of protection/discrimination relays at the installation.

It is possible to alter the settings for those, but be careful, because you do not want to exceed design limits for the installation.

Check the Engineers office and read how the system was set up, before altering and protection/discrimination relay settings.

Such alterations are best left to a Technician or Engineer who has wide experience in Power Distribution Systems, as if an error in the settings is made, damage to persons and equipment may be of major proportions.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply Score 1 for Good Answer
Associate

Join Date: Sep 2007
Posts: 54
Good Answers: 3
#2
In reply to #1

Re: Tripping of Incomer Breaker

09/04/2008 9:31 AM

Hello Spark,

I agree with you if the fault happened within the same transformer which is not our case. I believe that the system has two different transformers the first is 220/33 kV transformer; the second is to step down the 33 kV to 11 kV (i.e. 33/11 kV). The 11 kV side of the later transformer is the faulty one.

The question is whether each transformer has two breakers (one on each side) as per normal configuration/practice or not? If yes, the 33 kV breaker (Incoming breaker) of the 33/11 kV transformer is the one who should trip. Otherwise, a protection coordination study should be carried out to avoid tripping of the upstream breaker (220 kV) for faults at load side (11 kV).

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#5
In reply to #2

Re: Tripping of Incomer Breaker

09/04/2008 11:24 PM

Thanks, yes each Trx having two breaker, the relay setting and coordination done by ETAP, from the curve it shows every thing is correct, now we are checking the whole calculation once again and trying to do real time simulation for these model.

__________________
manirul
Register to Reply
Anonymous Poster
#3

Re: Tripping of Incomer Breaker

09/04/2008 10:55 AM

Under normal circumstances for a correctly graded protection system, a downstream fault on the 11kv side of the second transformer should not trip the incomer CB of the 220/33kv transformer. Areas to check are:

1.The integrity of the protection for the HV breaker to the 33/11kv transformer( that is if there is HV o/c protection), it could be that the relays picked up the fault but the breaker failed to trip or the relays never saw anything

2. The integrity of the protectin relay co-ordination for the network in question;

Regards,

Register to Reply
Active Contributor

Join Date: Aug 2008
Posts: 11
#4

Re: Tripping of Incomer Breaker

09/04/2008 10:58 AM

Under normal circumstances for a correctly graded protection system, a downstream fault on the 11kv side of the second transformer should not trip the incomer CB of the 220/33kv transformer. Areas to check are:

1.The integrity of the protection for the HV breaker to the 33/11kv transformer( that is if there is HV o/c protection), it could be that the relays picked up the fault but the breaker failed to trip or the relays never saw anything

2. The integrity of the protectin relay co-ordination for the network in question;

Regards,

__________________
Opportunity is missed by most because it is dressed in overalls and looks like work
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jmd (1); manirul (1); Sparkstation (1); TITO60 (1)

Previous in Forum: max current of capacitor   Next in Forum: Pump Motor
You might be interested in: Over-the-Side Heaters, Circuit Breakers, Load Centers

Advertisement