Thermal Sensitivity on Turbo Rotor Generator

09/06/2008 11:11 AM

Dear All

Could you advise me how to test and calculate the thermal vector due to thermal effect vibration on the turbo generator 3000 RPM, 237.5 MVA,

Based on GE paper, I just test for this generator with 2 test step.

Step 1. Make a constant field current with vary MW load

Step 2. Make a constant MW load with vary MVAR

GE specification if thermal vector limit within 2-3 mils or (50.8 - 76) mm, is not consider as a thermal sensitivity.

Based on GE spect, Test step 1, must test up to round cos phi 0.95 leading when test 1, and up to cos phi round 0.78 laging when test 2.

Due to the systems demand during synchronized to systems, we cant test up to 0.95 leading and 0.78 laging, but only cos phi 1 up to 0.8 laging,

as my calculation the thermal vector is 62 micron at bearing 5 and 66 micron at bearing 6.

Could you assisst me what is the conclussion and what is main problems that create vibration, its mechanical or thermal vibration ?

Vibration at cos phi 0.8 = 150 micron at bearing 6, and vibration at bearing 6 60 micron.

Thank you for your advise

Rgds

siswanto

__________________
LOVE FORUM AND DISCUSSION
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Thermal Sensitivity on Turbo Rotor Generator

09/09/2008 2:17 AM

There are many sources of vibrations on generator rotors. Mechanically, they could include poor balancing, cocked CRRs, cocked fans, blocking shifted, bearing oil issues, bearing metal issues, cracks developing, etc.

Thermally, the most common problem is some form of restriction in the winding. This could be as a result of inadequate allowance for winding expansion, blocking problems, 'sticky wedges' (where the winding catches against the wedges in one area, forming a bow), cooling unbalance, etc. Shorted turns, depending on what coil they're on, could also result in vibrations.

There are different ways of determining what the problem might be. Some are simple, some not so simple. But the best bet is to have an OEM engineer or a generator specialist on site to assist, or at least discuss the issue with them and get their ongoing advice. We have had many different gen rotor vibration issues, most of them interesting, if that's the word, and it is very difficult to give advice generically.