Mechanical Latch for HV Motor Contactor

09/11/2008 1:25 AM

Why does a HV Motor Contactor needs Mechanical Latch?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#1

Re: Mechanical Latch for HV Motor Contactor

09/11/2008 2:07 AM

The latched contactor is essentially identical in construction to a magnetically-held contactor. However, instead of relying on a continuously energized main coil to keep the contactor closed, the latched contactor utilizes a mechanical latch to hold the contactor closed. A magnetically held contactor remains closed as long as the main coil is energised.

For motors mechanical latched contactors are generally not taken as you will not want the motor to start utomatically once the power supply is resumed. Generally mechanically latched contactors are used for loads like lighting transformers where you want the system to resume operation whenever power supply is resumed. Sometimes some motors may also have this requirements depending on what the driven equipment is. In this case the mechanical latched contactor is better than magnetically held contactor because it is not dependent on continuous availability of power to the main coil of the contactor.

__________________
Atlas Shrugged - JGD
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Mechanical Latch for HV Motor Contactor

09/11/2008 6:47 PM

I agree they are not a good idea in general, but it is sometimes done on large MV motors because the starting current causes a severe voltage drop and they do not want the contactor to drop out during start. This is only done when the voltage drop is acceptable, essentially making the supply transformer into a saturable reactor for starting the motor. Usually on such systems, there are no other loads nearby that will be negatively affected. The control circuit must then be designed in such a way that if power does completely fail, the "Unlatch" coil of the mecahnically held contactor is always pulsed immediately upon re-energization just to be sure.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#3
In reply to #2

Re: Mechanical Latch for HV Motor Contactor

09/14/2008 1:05 AM

Thanks JRaef for the insight. Great help.

__________________
Atlas Shrugged - JGD
Register to Reply
Associate

Join Date: Aug 2008
Location: Dubai, United Arab Emirates.
Posts: 38
#4
In reply to #3

Re: Mechanical Latch for HV Motor Contactor

09/21/2008 2:35 AM

Dear Current Maarey & JRaef, I thank you both a lot for explaining me on this subject. I now know the operation of a Mechanical Latch using for Contactor. But still I want to why do we need to use this for a HV Motor Starter Contactor which is powered by DC for it's Contactor Coil? Thanks in advance with Best Regards.