Grounding of Systems over 1 KV

09/29/2006 4:35 PM

Here's the scenario:

13,200 Volt 3-phase/4 wire system is supplied from the local utility company. The service point is on the load side of cutouts at the top of a pole, located at the edge of the property.

Customer owned primary is then run down the pole (3-#2 copper, shielded, 133 percent insulation, Type MV-105) to a listed disconnect rated 600 amps and fused at 125 amps. The disconnect feeds a 2500 kva delta/wye transformer which steps the voltage down to 480/277.

Since the system supplied by the utility company is a 4-wire system, is it required to run a grounding conductor with the MV cable from the top of the pole to the disconnect and transformer? or since the "service point" is at the top of the pole, can the contractor elect to go with the proposed shielded cable (cable specs reflect use for an ungrounded system) and supply the premises with an ungrounding system and derive a grounded conductor/nuetral at the pad mounted delta/wye transformer?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2006
Location: Adirondacks of NYS
Posts: 136
Good Answers: 7
#1

Re: Grounding of Systems over 1 KV

10/01/2006 10:44 AM

I've done it that way. Derive the ground from the secondary side of the transformer. The utility acts as it's own inspector, do what they tell you. When you say shielded cable I think you really mean amoured cable from the pole to the switch.

__________________
If I hear hoofbeats, why don't I ever think a Zebra might be around?
Reply
Anonymous Poster
#2
In reply to #1

Re: Grounding of Systems over 1 KV

10/01/2006 11:31 AM

Actually, it is a shielded cable (3) installed inside of 4 inch PVC conduit. The customer owns the primary from the load side of the cut outs on the pole. I am not the contractor; I am the inspection authority. One of my inspectors have already approved the installation and the utility company subsequently energized the service.

The question was brought to my attention after the fact by an interested party and I'm trying to sort through it and make sure it meets the NEC. I can not find any requirement in Article 250 that requires, for systems operating at over 1kv, to be grounded where supplied by a utility system that is grounded. Article 250.20 & 250.24 are very clear that it is required for systems operating at 50 to 1000 volts, but grounding is only an option, for over 1kv.

Thanks,

Tim

Reply
Power-User

Join Date: Aug 2006
Location: Adirondacks of NYS
Posts: 136
Good Answers: 7
#3
In reply to #2

Re: Grounding of Systems over 1 KV

10/01/2006 3:02 PM

Like I said, the Utility is generally it's own inpector. They deal with that level of power everyday and have worked out procedures and policies that insure safe operation of a power distribution system. Most Inspectors are not well versed in the power distribution side of things. They don't see it or work with it often enough. NEC trusts the Utility to make the correct connection decisions (without an outside inspector) for over 1KV applications. Most 13,800V lines in this area are not grounded, (other than static lines) so your statment of article 250 "systems operating at over 1kv, to be grounded where supplied by a utility system that is grounded" is quite correct and you should do as the Utility recommends. The Utility would not have energized the equipment if the thought it might cause an outage of the system.