Here's the scenario:
13,200 Volt 3-phase/4 wire system is supplied from the local utility company. The service point is on the load side of cutouts at the top of a pole, located at the edge of the property.
Customer owned primary is then run down the pole (3-#2 copper, shielded, 133 percent insulation, Type MV-105) to a listed disconnect rated 600 amps and fused at 125 amps. The disconnect feeds a 2500 kva delta/wye transformer which steps the voltage down to 480/277.
Since the system supplied by the utility company is a 4-wire system, is it required to run a grounding conductor with the MV cable from the top of the pole to the disconnect and transformer? or since the "service point" is at the top of the pole, can the contractor elect to go with the proposed shielded cable (cable specs reflect use for an ungrounded system) and supply the premises with an ungrounding system and derive a grounded conductor/nuetral at the pad mounted delta/wye transformer?
Thanks