Testing Methods & Standards for Brass Spring Check Valve??

09/18/2008 5:48 AM

Dear All,

I got a brass spring check valve and try to test it's function & guality.

It looks good and could prevent the water flow back.
However, when the water volumn is less than 1 kg, it start to flow back.

I don't know if this usually happens to all brass spring check valves.
Could anyone kindly advise the testing methods & standards for Brass Spring Check Valves.

Thanks & Regards,

Jones

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
United Kingdom - Member - New Member

Join Date: Aug 2008
Location: UK
Posts: 56
Good Answers: 5
#1

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/18/2008 9:39 AM

In a properly designed check valve there should be little or no flow back once the valve is closed.

You must have a defective check valve there.

Register to Reply
Member

Join Date: Jul 2008
Posts: 8
#2
In reply to #1

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/18/2008 8:04 PM

Dear Frank787

Thanks for your immediate assistance.

But how could we define the "little"?

I have no testing methods or standards to check if it is defective.

Could anyone advise?

Jones

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/18/2008 11:15 PM

There are standards available for this, for example you can always rely on API 6D where in general all the requirements and tests to be carried out are covered.

(Usually no visible leakage at minimum 1.1 rated pressure)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Member

Join Date: Jul 2008
Posts: 8
#4
In reply to #3

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/18/2008 11:23 PM

Dear SB,

Thanks. I will check API 6D.

By the way, I have question about 1.1 rated pressure.

It means 1.1 Mpa, right?

thanks.

Jones

Register to Reply
Participant

Join Date: Sep 2008
Posts: 2
#5
In reply to #4

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/19/2008 7:05 AM

Dear Jones,

There is dedicated standard available for brass-bronze gate globe & check valves,i.e.MSS-SP 80.In this u can get design,testing mathod,test pressure w.r.t.rating .

rated pressure means : e.g. if ur valve rating is 150#,then your valve will have a rated pressure of 19 bar,as per asme b 16.5.this value is selected based on max.ratio of pressure/all.stress at temp. from table.

Register to Reply
Active Contributor
Hobbies - Musician - New Member

Join Date: Jul 2007
Location: Titusville,Fl.
Posts: 21
#6

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/19/2008 8:16 AM

I had a similar problem on a potable water system and on disassembling it to do a visual inspection,found that the spring had deteriorated which lessened the tension against the disc,which also was worn bad,and there was debris inside the chamber the seat was pitted,and the labor involved with the removal of this particular valve was intense,so I just replaced it.It was'nt very much, I think it was less than $100 for a 2 inch.It was a common and easily availiable valve,and I had ordered it and had it on board before I did anything.But, if your valve is very expensive to replace and is on a critical system,my method probably won't work too well. hope you solve your problem,Skip

__________________
Hope for the best,Expect the worse,Take whatever comes
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#7

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/19/2008 9:26 AM

On an earlier series of fire trucks, we spec'd. spring loaded check valves for fast filling. The original design were not well sealing, and always leaked. When we forced the manufacturer to change to better sealing valves, the problem went away except one side of one truck. The four inch pipe was long enough to reach into to check for the problem. It seems a frog had crawled into the supply hose attached to the hydrant. When the driver filled his truck, the frog got half way through the check valve. When I reached into the pipe I found the other half.

How was your day?

__________________
Bob
Register to Reply
Power-User

Join Date: May 2008
Posts: 380
#8

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/19/2008 2:39 PM

I think it normally happens:i should work a little with some abrasive paste,and clean, it will finish any leakage at all.

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#9

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/20/2008 5:14 AM

1.1 rated pressure means if the valve is rated for schedule and say the pressure rating is 20kg/cm2 (3000PSI) then the testing should be done at 22kg/cm2

Pl note this is not the pressure at which the system is working but what the valve is designed for.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Power-User

Join Date: May 2008
Posts: 380
#10
In reply to #9

Re: Testing Methods & Standards for Brass Spring Check Valve??

09/20/2008 12:50 PM

Idon't try to remember the exact values and rarely i look for in tables but i remember the air compressors gauges: 14 kg/cm2 is almost 200psi so 3000psi is not 20kg/cm2.The rest of your comment is very useful to me:i thought it was like in hoses test pressure ¿four times? work pressure.-

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Testing Methods & Standards for Brass Spring Check Valve??

02/22/2024 10:05 AM

It sounds as though the <...testing methods...for Brass Spring Check Valves....> are already being deployed. They are, after all, relatively simple things.

One assumes that the valve is installed such that gravity will close it when there is no flow, is that right?

<...water volumn is less than 1 kg...>

What does that mean?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856