MCB OK and MPCB not OK for VFD

09/20/2008 12:25 AM

I am using a 15HP and 30 HP VFD.Here I MPCB is connected before VFD which is (the MPCB)tripping continuously.This was changed with MCB.It is now fine and running properly without tripping..Can I know Why??

Anyone reply immediately

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#1

Re: MCB OK and MPCB not OK for VFD

09/20/2008 12:54 AM

http://cr4.globalspec.com/thread/25466

Check this.

On VFDs I would size your breakers for the conductors and leave the motor protection to the drive and possibly add a line filter between the drive and motor.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply Score 1 for Good Answer
Participant

Join Date: Sep 2008
Posts: 2
#2
In reply to #1

Re: MCB OK and MPCB not OK for VFD

09/20/2008 5:20 AM

Thankyou

How to calculate the Line reactor for my 30HP motor

Register to Reply
Power-User

Join Date: Jan 2008
Location: Silvis, IL (Quad Cities)
Posts: 141
Good Answers: 5
#3
In reply to #2

Re: MCB OK and MPCB not OK for VFD

09/20/2008 9:58 AM

Hire a competent electrical engineer or a qualified electrician.

__________________
Perfection is achieved, not when there is nothing left to add, but when there is nothing else to take away
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#4
In reply to #2

Re: MCB OK and MPCB not OK for VFD

09/21/2008 5:00 AM

The Line reactor will reduce earth leakage peak currents caused by the inverter switching pulses charging the motor cable capacitance. This can cause inverter 'overcurrent' trips (nuisance). Unless you have 100m+ of armoured cable you may not really need this, but, if required, a value of 1mH and a current rating to cover the motor FLC will suffice and set inverter switching frequency to a lower level, say 3 - 4kHz to stop choke core overheating. However, I think the MPCB is unlikely to be affected by the inverter output to the motor.

The MPCB is likely affected by the 'rectifier' current shape at the inverter supply, so it may be unsuitable for an inverter load as opposed to a sinusoidal motor load. You can improve the waveform by adding an input choke or a DC choke if this isn't included in the inverter already. Normally though, select cable for inverter input (RMS) current and protect accordingly with fuses or CB. The motor overload should be taken care of in the inverter but not all offer good single phasing proection. Better would be thermistor protection in the motor if the plant operation is critical.

Likely questions:

What is the inverter rated input current? (On the nameplate)

What is the MPCB / MCB rating? (Current and type)

What RMS current are you drawing in operation?

__________________
Something new every day!
Register to Reply
Power-User

Join Date: Jul 2008
Location: India
Posts: 452
#6
In reply to #4

Re: MCB OK and MPCB not OK for VFD

09/21/2008 2:14 PM

we have the frequent problem in drives because of power serge.

this 3 phase line reactor will help us or not?

how much it cost?

please inform me

__________________
thoughts becomes things.
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#7
In reply to #6

Re: MCB OK and MPCB not OK for VFD

09/21/2008 4:04 PM

What kind of problem does the power surge give your drives?

Overvoltage trips?

Input bridge failure?

Transistor failure?

An input reactor and varistors will definitely offer some protection from surge but it will depend on the total energy and duration of surge as to exactly how much this helps. You can configure some drives to disconnect from supply before the voltage goes too high if you use choke to slow down the charging rate. An input choke coupled with a DC choke for AC drives is a near best scenario if you have severe problems and failure of semi-conductors.

I would need more details (supply V, Hz, kW, type of drive etc, type of surge cause)to be able to recommend some options if you want some parts recommendations - not sure how you do this via this forum??

__________________
Something new every day!
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#8
In reply to #7

Re: MCB OK and MPCB not OK for VFD

09/21/2008 5:11 PM

I believe one advantage that we targeted with the filters was to subside the voltage spikes created in remaking the alternating wave and protect the motors from breakdown voltage and keep the drive from piercing the motor insulation.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: MCB OK and MPCB not OK for VFD

03/29/2023 7:32 AM

<...how much it cost?...>

The answer to this question requires a Purchasing Officer and a telephone.

Invitation declined.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #2

Re: MCB OK and MPCB not OK for VFD

09/21/2008 10:03 AM

A company called MTE has a good tables for industor sizing.

http://www.mtecorp.com/index.html

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

harishchanna (1); Kilgore Trout (2); MalcolmK (2); marcot (1); PWSlack (1); sandeep lokhande (1); Shawn_V_Elect (1)

Previous in Forum: Liquid Rotor Resistance   Next in Forum: Selection of transformer
You might be interested in: Circuit Breakers, Thermal Overload Relays, Computers

Advertisement