electrical engg

09/22/2008 2:54 AM

what is th difference between H.T motors & L.T motors.the same Kw rating motors are used as either H.T or L.T in some cases.why it is.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#1

Re: electrical engg

09/22/2008 5:32 AM

The basis of classifying whether a motor is HT (HV) or LT(LV) is based on the voltage level at which this motor is fed power.

The classification of voltage level as LV, MV, HV, EHV is defined by various standards. Please note that there are some differences between them eg as per IEC (being followed in in large numbe rof countries) 400V/415V/440V is termed as LV whereas in India 415V is termed as MV.

As far as issue for classifying the same rating of motor as LV or MV is concerend this happens in borderline cases. It depends upon the client and the consultant, also on the power system distribution design, whether to feed a particular rating say 200kW from 400V system or from MV system of 3.3kV or 5.5kV or 6.6kV. Acordingly the motor becomes LV or MV.

__________________
Atlas Shrugged - JGD
Register to Reply
Participant

Join Date: Sep 2008
Posts: 3
#6
In reply to #1

Re: electrical engg

09/29/2008 5:46 AM

thank u for ur valuable clarification.

Register to Reply
Anonymous Poster
#8
In reply to #1

Re: electrical engg

06/28/2010 1:36 AM

i am just confused, in electrical panel its written "DANGER HIGH VOLTAGE" whereas its only 220V,

shokran

rma

Register to Reply
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#2

Re: electrical engg

09/22/2008 6:25 AM

they have different voltage output. thats hteir difference.

Ht and lt can be the same power rate. no problem. but they are use differnt equipment which has different voltage rate.

and why these equipment have different voltage rate? you will be curious next step I think.

the simple answer is, they have different purposes.

Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#3

Re: electrical engg

09/22/2008 10:38 AM

Hi sabarinathsingh,

The basic concept is the higher the voltage the current is lower for the same wattage and the conductor size has to be large to carry higher current. With lower voltage the transmission loss and heating losses will also be high.When we design a motor with higher voltage the insulation level has to be more and the safety to operators to be ensured. More over the system voltage has to be changed if you use some particular motor with higher voltage. So all the parameters like size of motor and system voltage and safety of operation and financial implication are considered to arrive at a decision regarding voltage of motor for specific purpose.

Register to Reply
Anonymous Poster
#4

Re: electrical engg

09/23/2008 12:02 AM

Hai, The LT and HT ratings are classified mainly on the voltage ratings for the same capacity motors. The difference between them is voltage and also the type of Insulation used. As in the case of HT there more care has to be taken against High voltage and also against thermal overheat. Thanks, Vinod

Register to Reply
Anonymous Poster
#5

Re: electrical engg

09/23/2008 3:50 AM

Dear,

please may be noted that normally, to avoid large current in LT, HT (3.3KV to 11 KV normally) Motor are preferred. If you increase the voltage for the same KW, FLA (Full Load Ampere) will be much lesser, so its maintenance, as well operational aspects are much better. In the industries normally above 200 KW are using as 6.6 KV or above.

You can easily calculate the current for higher voltage rating at same KW / KVA / MVA (in case of Trafo).

Hope you will understand.

Regards,

J. P. Shukla

Register to Reply
Participant

Join Date: Sep 2008
Posts: 3
#7
In reply to #5

Re: electrical engg

09/29/2008 5:58 AM

well,thank u.but in our case,there are 3 motors of 200 Kw.2 of them are H.T(6.6Kv) & 1 is L.T(415v).all are used for same purposes (in process point of view).so i am in doubt.when we use H.T the F.L.C will be less.so we can use all that 3 motors as H.T.but it is not so.why?

Register to Reply
Anonymous Poster #1
#9
In reply to #5

Re: electrical engg

04/16/2012 5:47 AM

Hii,

Normally we consider LT(440V and below) and HT (Above 440V) in the case of motors. But some considers LV, MV and HV. But for some testing purposes its makes confusion(in my case Polarization index test - calls for HT motors). So my question is where this MV will fall into - LT or HT. Is there any standards mentioning that?

Thanks in advance

Register to Reply
Register to Reply 9 comments