Calculating Power Consumption

09/22/2008 5:41 PM

I want to determine power consumption of a 3 phase motor. I have measured voltage and current on all three legs.

Is there a way to determine the actual power factor from these numbers?


Chris

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Calculating Power Consumption

09/22/2008 5:47 PM

There are meters that clip on the circuit and measure the PF. Google PF measurement.

Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#2

Re: Calculating Power Consumption

09/22/2008 6:27 PM

http://cr4.globalspec.com/thread/25669#comment270757

This helped me--Amp reading times 1.732.

Mark 684 received a good answer and I believe that North of 60 also deserves one--Read up and cross reference them and vote if it helps you.---GOOD STUFF!

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Reply
Associate

Join Date: Aug 2007
Location: New Delhi, India
Posts: 33
#3

Re: Calculating Power Consumption

09/23/2008 5:53 AM

Power in 3 phase = √3 V I CosØ

(V is line voltage and I is line current, for delta connection line voltage would be voltage between two phases & Line current current would be √3 times any phase current. Ideally all 3 phase currents should be equal. But to know the approx power you can take the average of three.)

If you know the voltage and current you should also know at which power factor the motor is running. Use a pf meter to determin the pf and using the above formula calculate the power.

__________________
Ashish Gupta
Reply Off Topic (Score 5)
Anonymous Poster
#4

Re: Calculating Power Consumption

09/24/2008 12:17 AM

Hai, The 3 - phase power can be measured by following expression: P=Root(3) x VL X IL X COS(p.f) Where VL - Line voltage of the supply IL - Line current Cos(p.f) - Power factor The power factor measurement can be done by 2-Wattmeter method (care should be taken for using LPF or UPF meters) Thanks, Vinod

Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5
In reply to #4

Re: Calculating Power Consumption

09/24/2008 6:53 AM

Without suitable power metering for exact measurement, an estimate could be made by taking the full load power factor on the nameplate to estimate no load current and factoring in efficiency or by motor speed.

i.e. Io = Iflc * (sq root (1- (cosphi)2))

e.g. 5kW 90% eff 10A flc motor cos phi (nameplate) = 0.8 squared = 0.64. Then 1-0.64 = 0.36. Then sq root of 0.36 = 0.6. Io = 10A 8 0.6 = 6A.

If this motor drew 8A, then at half load approx 2.5kW, at 90% eff then consumption roughly 2.75kW.

Motor load can also be assessed by motor speed if you have a reliable tacho.

e.g. 5kW motor nameplate = 1430 Motor speed = 1465 therfore half load again etc. In my experience, true full load speed is normally more than nameplate to the order of 80% of slip. So I would say if 1430, real full load speed could be 1444rpm (80% of stated slip)

Any input from motor designers??

__________________
Something new every day!
Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#6

Re: Calculating Power Consumption

09/24/2008 2:29 PM

No, not without at least one other value; either phase angle or watts, however you could ratio your measured values to the stated nameplate values for this motor and come close. [(Vn*An/v*a)*Hpn]/746 = watts(approx).

p.f.=watts/va

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#7

Re: Calculating Power Consumption

09/24/2008 3:33 PM

The relation between values is the following:

S = U * I * pf * eff * sqrt(3) = P * pf

where

S = apparent power [kVA] (input power)

U = voltage (line-to-line) [V]

I = current drawn [A]

pf = power factor [-]

eff = efficiency [-]

P= active(real) power [kW] (input power)

The input power includes output mechanical power at the shaft (torque x rotating speed) + all losses in the machine. The losses are included in the efficiency ( eff = output power /(ouput power + losses).

You measured U and I. In order to be able to determine the power factor you need additional data: torque + speed + efficiency.

If the measurements were made at full load (rated, nominal) , some recommended values are given below. At lower load, the values are lower.

It the list below, the rating is given in HP ( 1 HP = 746 W for USA, 1 HP = 736 W international) (output mechanical power) power factor and efficiency are indicated in [%]. In the formula indicated earlier, values should be entered as decimal.

MOTOR EFFICIENCY AND POWER FACTOR REQUIREMENTS

HORSEPOWER

EFFICIENCY

POWER FACTOR

1 hp85.5 pct.78.0 pct.
1.5 hp86.5 pct.78.0 pct.
2 hp86.5 pct.83.0 pct.
3 hp89.5 pct.80.0 pct.
5 hp89.5 pct.80.0 pct.
7.5 hp91.7 pct.81.0 pct.
10 hp91.7 pct.82.0 pct.
15 hp92.4 pct.82.0 pct.
20 hp93.0 pct.86.0 pct.
25 hp93.6 pct.84.0 pct.
30 hp93.6 pct.83.0 pct.
40 hp94.1 pct.86.0 pct.
50 hp94.5 pct.87.0 pct.
60 hp95.0 pct.86.0 pct.
75 hp95.4 pct.87.0 pct.
100 hp95.4 pct.90.0 pct.
125 hp95.8 pct.88.0 pct.
150 hp96.2 pct.86.0 pct.
200 hp96.2 pct.87.0 pct.
over 200 hp96.2 pct.87.0 pct.

The values are those recommended as minimal in the US for a "Energy Star" qualification.

__________________
Scientes et audaces fortuna juvat !
Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#8
In reply to #7

Re: Calculating Power Consumption

09/24/2008 3:48 PM

The theory is good but beware of using assumptions of pf when at part load.

The pf decreases dramatically with load e.g. 0.9 at full load, 0.7 at half load.(c. 5kW)

Many suppliers do not list pf below half load as the pf is so poor.

So, if the motor is not near fully loaded and known to be, be aware the calulated result may have much more error in overestimating power consumption which is, in effect, apparent only.

__________________
Something new every day!
Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#9
In reply to #8

Re: Calculating Power Consumption

09/24/2008 4:14 PM

You are absolutely right. The pf is the ratio of real (ohmic) power vs apparent power. the reactive power requirement is basically the power required for magnetization and is nearly constant along the load spectrum ( from no-load to full load) while the real power has to cover the output power (dependant on load) + losses ( some dependent on load ( losses in windings) and other nearly constant (mechanical).

The numbers given were for the full load situation.

__________________
Scientes et audaces fortuna juvat !
Reply
Anonymous Poster
#10

Re: Calculating Power Consumption

09/24/2008 5:01 PM

It is very easy to determine the Power, Current, Voltage, Power Factor for this Formula.

Power (KW) =1.732*Voltage*Current*Power factor.

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); ashuashi (1); CJMcGill (1); Kilgore Trout (1); MalcolmK (2); tomad (2)

Previous in Forum: Transformer Fuse Sizes and Types   Next in Forum: the right size for electrical cable

Advertisement