Effect of harmonics from SCR drive on other components

09/26/2008 5:13 PM

Dear members

I want to know the effect of harmonics produced by an SCR drive on the local distribution network (consisting of tube lights, metal halide lamps, air conditioners, computers. battery chargers, fans, etc.). At present the SCR drive is supplied by a separate transformer. The distribution network is supposed to be connected to the same transformer by taking a tap from SCR panel Busbars.

Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Control Engineering - New Member China - Member - New Member

Join Date: Sep 2006
Location: CHINA
Posts: 2945
Good Answers: 14
#1

Re: Effect of harmonics from SCR drive on other components

09/26/2008 10:14 PM

How much harmonic depends on your scr equipment quality.

this will interference on computer, chrger etc electronic facilities. some times, electronic ballast of tube and hlidelamjpe are also interferenced it.

although now they are not connect to a same transformer, but the harmonic wave can go throgh electric net.

so the best bet is adding a filter, shield and good chases to reduce the interference.

Register to Reply
Commentator
Indonesia - Member - Member from Indonesia Hobbies - Fishing - New Member Engineering Fields - Electrical Engineering - Member

Join Date: Aug 2008
Location: Batam, Indonesia
Posts: 85
Good Answers: 1
#2

Re: Effect of harmonics from SCR drive on other components

09/27/2008 3:52 AM

"The increased use of computers and solid state electronics in the modern workplace has been accompanied by an increase in the presence of destructive harmonics within electrical distribution systems. Symptoms of destructive harmonics include, but are not limited to: nuisance tripping of circuit breakers, blown fuses, failed motors, and overheated transformer windings and neutral conductors. Since harmonics are often accompanied by a temperature rise, thermography can be used to detect evidence of their presence. This paper will discuss the causes, effects, and symptoms of harmonics as well as techniques for dealing with harmonics"

"Sites that utilize electronic drives and power transmission systems with six and twelve pulse SCR's commonly have similar problems. These types of SCR drive systems also cause distorted currents which in turn cause overheating on cabling and transformer windings"

Source:

www.irinfo.org/Articles/02_01_2007_handlin.html

__________________
Fear of God is the beginning of knowledge, God bless you.
Register to Reply Score 1 for Good Answer
Associate
Hobbies - DIY Welding - New Member Popular Science - Weaponology - New Member

Join Date: Nov 2007
Posts: 29
#4
In reply to #2

Re: Effect of harmonics from SCR drive on other components

09/28/2008 5:58 AM

There is some very good info in that paper!

Register to Reply
Participant

Join Date: Sep 2008
Location: Dayton, Ohio
Posts: 2
#3

Re: Effect of harmonics from SCR drive on other components

09/28/2008 12:35 AM

I work in a data center, we had a terrible time with harmonics from EMF.

The company finally had to have the intire raised floor area grounded at the SRGs and to the main building ground.

They also added electrical protection from lightening as they were doing this.

The bleeding of electrical harmonics and EMF was so bad, you could change a defective fluorescent bulb, as I touched the bulb, the bleeding surge would cause the nearest emergency door alarm to ring.

They have now cut back on the problems of blade servers and cabinet power supplies from frying. I hope this helps.

__________________
Well, there's your problem...
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #3

Re: Effect of harmonics from SCR drive on other components

09/28/2008 9:19 AM

That problem is often seen in office buildings. It is typically caused by bad wiring of the neutral conductor. Incompetent electricians do not keep the line and the corresponding neutral together from the breaker box up to the load. This usually happens during wiring modifications where branches are pulled from existing wiring almost randomly. They often tap on the first neutral they find even if it doesn't corresponds to the line they are using. This created large inductive loops in the electrical supply. Inductive loops are antennas, and you know what they do. Also, the inductive loops produce unwanted voltage drops which can affect the loads.

Adding grounds can minimize this effect but is it the wrong way to do it as it encourage the ground wires to become neutral conductors conducting the imbalanced current between the line and the neutral(s) wires.

If you really want to solve this problem, re-wire the area properly with three conductors cables (L,N,G) and minimize branching.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Register to Reply 5 comments