Junction Box Rules

09/29/2008 8:01 PM

If junction box puts in Class 1 Division2 region, if only stipulated NEMA 4X, whether needs the extra request to have to tally increases safely? Whether there is stipulation laws and regulations?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Anonymous Poster
#1

Re: Junction Box Rules

10/01/2008 7:54 AM

I'm not sure what you are asking in your question. If you are asking if a nema 4x junction box can be used in a classified area the root answer is yes. The box itself is not the issue though is it? It's the equipment you put inside the box that makes the difference. If none of the devices in this junction box are arcing devices, it can still be installed in your classified area. If there are arcing devices present the box either needs to be explosion proof or you need to purge the box to insure the presence of ignitible gases is non-existant.

Register to Reply Good Answer (Score 2)
Power-User

Join Date: Feb 2008
Location: Northeast Ohio, USA
Posts: 267
Good Answers: 9
#2

Re: Junction Box Rules

10/02/2008 7:03 AM

You have specifically asked about Class 1, Division 2 locations. In these locations, NEMA 4X junction boxes are acceptable. In Class 1, Division 1 locations, they are not. You would need NEMA 7 (explosionproof) junction boxes, the fact notwithstanding that they have no "make-or-break" apparatus in them, they are still so designated.

Actually, in the Division 2 locations, you can use NEMA 1, general, purpose boxes unless your application requires the NEMA 4x enclosure for weather protection or some other extenuating circumstances.

__________________
All that is necessary for the triumph of evil is for good men to do nothing. - Edmund Burke
Register to Reply Score 1 for Good Answer
2
Active Contributor

Join Date: Jun 2008
Location: Dartford, kent , England
Posts: 11
Good Answers: 1
#3

Re: Junction Box Rules

10/02/2008 10:57 AM

I am in england and we work to the Atex directive for hazardous area... Normal I/P protected junction boxes can be used in a hazardous area if they only contain intrinsically safe ciruits... the barriers or galvanic isolators must be located in the safe area.. these junction boxes should be labelled up as containing intrinsically safe circuits and all cables should be with a blue outer sleeving to identify they are intrinsically safe circuit / loops. All other equipment should be certified for hazardous area use and be either flameproof or increased safety.. which are the common means of protection. They must all be certified for the area zones, the failure T temperature and the gas / dust type. Hope this helps as i have no idea from your question what equipment is being installed.

__________________
Raise to the challange and do it safely
Register to Reply Good Answer (Score 2)
Register to Reply 3 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jeffweeden (1); The Commoner (1)

Previous in Forum: DCT Instruments, Sensotec (Honeywell) J Series Help??   Next in Forum: energy tester

Advertisement