10/04/2008 4:20 AM
CAN ANYBODY EXPLAIN TO ME THE REASON WE USE A 4-20mA CONVERTER ON A THERMOCOPLE.
Re: WHY DO WE USE A mA CONVERTER ON A THERMOCOUPLE?
10/05/2008 1:48 AM
Coz T/C Output is in MV and may b u r DI Module accepts 4-20 ma
Regards
jose
10/06/2008 5:12 AM
I can think of 3 reasons
a) Distance. If cable length is too long, you may have problems with a mV signal
b) Receiving device only has mA inputs (or it will be cheaper to use one)
c) To avoid laying special compensating cables or to use exisiting spare instrument cables
Steve
MTL Instruments
www.mtlblog.com
Bad English is Bad for Business
10/10/2008 1:27 AM
because of the thermocouple is working under the principle of " seeback effect " and peltier effect,thomsan effect
thermoucouple generates the milli volt output only but DCS expectation is in terms of voltage
V=i*r
24 = (4-20mA)*250 -----------> gives the 1 - 5 v it is happening at the DCS by converting the ( mA to v by A/D converter )
DCS accepts 1 - 5 v only
thats while we are converting the mV to mA by ( voltage to current converter )
at TT
u know how the RTD output is converted to the 4 to 20 mA by wheatstone bridge circuit if the RTD type is PT 100 type .
the unbalance in the wheatstone is converted into millivolt that is converted into current mA
in wheatstone bridge ressistance at three side is connected equal value 100 ohms and remaining sensor side will connected
11/23/2008 12:21 AM
For me,
The T/C output is in mv.
and we may get loss of signal over long length of cable.
It also depends upon I/P module use for indication or control.
12/15/2009 1:02 AM
i dont understand I/P module
12/15/2009 3:28 AM
I/P = input.
08/22/2011 5:44 AM
CR4 ADMIN: Deleted Post
Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.
03/03/2010 5:22 PM
hi,
I think it is because T/C is always used to measure very high tempratures and so we must put the receiver of the signal of it far away from this hazardous area and so usually we use a long cable to connect between them and for the mv signal that T/C produces, it will be vanished before it arrives to the receiver so we must convert it to a mA signal.
Maged Anter
01/03/2011 7:35 AM
the situation is follows:
if any problem happens on plant , espicellay temperature value is zero thermocouple indicates the value of 4mA, where as the the thermocouple is fault it indicates the zero mA. Mainly used for differntiating d temperature o/p and thermocouple o/p
if its wrong kindly reply...
08/29/2023 7:24 AM