Whats the minimum size cleanout for a 6"pipe?

10/04/2008 1:34 PM

Greetings

I live in the U.S.A in the fairfied couny.Do anyone know what is the minimum cleanout for a 6" pipe?Thanks in advance for any and/or all help

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Whats the minimum size cleanout for a 6"pipe?

10/04/2008 8:50 PM

It seems from another post that the adopted plumbing code in Fairfield County is the International Plumbing Code. As such - the minimum clean-out for a 6" pipe is 4" - See excerpt below:

708.7 Minimum size. Cleanouts shall be the same nominal size as the pipe they serve up to 4 inches (102 mm). For pipes larger than 4 inches (102 mm) nominal size, the minimum size of the cleanout shall be 4 inches (102 mm).

There are a couple exceptions though for "p" traps, stack clean-outs, or cast-iron clean-outs. Do any of these three items apply?

Register to Reply
Member

Join Date: Oct 2008
Posts: 6
#2
In reply to #1

Re: Whats the minimum size cleanout for a 6"pipe?

10/04/2008 9:59 PM

Greetings

no the items does not apply.Thank you very much for your help.

Register to Reply