Member

Join Date: Sep 2008
Posts: 6

Locked Rotor Current

10/10/2008 1:14 AM

Hello,
Can anyone help me to find out the rated current/locked rotor current & load factor of a 15KW motor which is connected to 415V ac.Estimated full load current & maximum demand are 26Amps.Load diversification=.06.Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: to find locked rotor current

10/10/2008 5:11 AM

Apply a multimeter between phase connections of a single winding, set to ohms, or possibly milliohms. Divide the resistance figure into the supply voltage. Bingo.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2
In reply to #1

Re: to find locked rotor current

10/10/2008 7:22 AM

A rule-of thumb: the locked-rotor current is 5 times the full-load current for direct-on-line starting.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Member

Join Date: Sep 2008
Posts: 6
#3
In reply to #2

Re: to find locked rotor current

10/10/2008 7:27 AM

Thank you.It was helpful.

Register to Reply
Anonymous Poster
#4

Re: Locked Rotor Current

10/11/2008 7:22 AM

The NEMA Standard MG- 1 has recommended the maximum locked rotor current of single-speed three phase motors for the various rotor designs B, C, and D, for various recommended torque values. These have been derived for a 415 V a.c. system and are shown as following:

20 hp (15KW) ------------ 178A (locked rotor current)

Also typical rated power factor for this rating is 0.86, as you know power factor in motor starting duty is very low.

--------------------------------------

Creative thinking is enjoyable, Then think about your surrounding things and other thought products.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Locked Rotor Current

10/11/2008 1:38 PM

LRC is normally 6 times rated current+-20%.Usually it is +tolerance.If full load current is 26A then LRC is between 156 Amps-187.2 amps.It is independent of other parameters but depends upon the motor design .Duration depends upon the load inertia.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); nesubra (1); PWSlack (2); veronica (1)

Previous in Forum: Name This Tube!   Next in Forum: Cost of IGBT

Advertisement