Motors Demand Factor Tables

10/13/2008 2:51 AM

Hi,

Could anyone please tell me where I can find tables for motor demand factors in order to size the MCC panel feeder ?

Thanks.

Register to Reply
Pathfinder Tags: Motors Demand Factors
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motors Demand Factor Tables

10/13/2008 10:55 AM

Well, they could be created by studying the specific installation drawings and looking at the usage characteristics or predictions.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Oct 2008
Posts: 5
#2
In reply to #1

Re: Motors Demand Factor Tables

10/13/2008 11:02 AM

thanks for your reply, but aren't there any guidelines for these factors, any average values from any standard?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3
In reply to #2

Re: Motors Demand Factor Tables

10/13/2008 4:24 PM

There are no "written guidelines" because every location is different. You must do the load calculations to determine the required panel size. The NEC provides section 220 to apply when making these calculation. If you are in another location, apply the codes for that area. If you are the designer, then you should know whether the motors will have any diversity or not.

Register to Reply
Member

Join Date: Oct 2008
Posts: 5
#4
In reply to #3

Re: Motors Demand Factor Tables

10/14/2008 1:35 AM

Thanks for your reply, section 220 in the NEC provides the calculation for lighting & receptacles circuits and their demand factors, but it didn't mention anything about motor branch circuits, however, section 430.26 mentions that the demand factor for motors feeders are based on experience and historical information from similar installations. In our project we follow the NEC but I need any guidelines from any other specifications as I do not have any information about our installation.

From my information, the demand factor is a multiplication of two factors.The utilization factor (because motors are rarely operated at their full load) this factor is usually from 0.75 to 0.8.

The other factor is the simultaneity factor (if the motors are not operated together at the same time).I have no idea about the range of this factor so I need any guidelines from any specifications.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #4

Re: Motors Demand Factor Tables

08/21/2024 10:48 AM

The best bet, then, is to find a Mentor at the facility who can help further.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856