Insulation Test Problem

10/14/2008 10:11 AM

After isolating one of our machines from the main switch room, then from the machine's isolator, a pre voltage and current check was done on the isolator line side before insulation test could be done on the main supply cable. The results are listed below as measured with a multimeter and clamp meter.

1. Line to Earth Test.

a. Line 1 (Red Phase) - Earth Volts = 0.50V

b. Line 2 (White Phase) - Earth Volts = 3.960V

c. Line 3 (Blue Phase) - Earth Volts = 3.50V

Line to neutral test had similar results.

2. Line to Line Test.

a. L1 to L2 = 3.873V. b. L2 to L3 = 7.34V c. L3 to L1 = 3.429V

3. Current Test.

a. L1 = 0.17A. b.L2 = 0.42A. c. L3 = 0.25A.

4. Questions.

Is it safe to carry on with insulation test at the presence of these leakage parameters?

Because of the presence of voltage and current at the line side of the isolator, insulation test of 1000Vdc and 500Vdc was not done. I though in case it would have a bad feedback on the insulation tester and may damage it.

What are the standards (AS/NZS, British, others) regulating the minimum control of leakage voltages and currents after isolation?

Your assistance and advice would be great.

Thank you and kind regards,

Ron

__________________
Kind regards, Ron
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#1

Re: Insulation Test Problem

10/14/2008 8:41 PM

It is actually quite common to see this with digital multimeters. I would suggest checking the circuits with an analog meter.

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply
Guru

Join Date: Feb 2006
Location: Piney Flats, Tennessee
Posts: 1740
Good Answers: 23
#2
In reply to #1

Re: Insulation Test Problem

10/15/2008 12:23 AM

I like the new methods of construction for factorys today when they use wiring they use is 2 sizes above the requirements or code so you never under power a piece of equipment and the line don't get hot. The worry of power loss in the line or bleed thru the insulation is not a high concern anymore.

__________________
If you never do anything you never have problems.
Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#3
In reply to #1

Re: Insulation Test Problem

10/15/2008 7:48 AM

Switchman,

Thank you for the advice, I will try with analog meter and compare the results.

__________________
Kind regards, Ron
Register to Reply
Anonymous Poster
#4

Re: Insulation Test Problem

10/15/2008 9:04 AM

Induced voltages on de-energized ungrounded equipment is normal in the presence of other energized equipment. It is best to ground one end of whatever you are testing to minimize potential stored.

Please correct me if I mis-interpret your terms,

You are trying to test a generator, a surge tester can do a DC winding insulation to ground resistance (hipot or megger) and a ringing comparision of the windings which would tell if there are shorted turns in the coils. A portable 12kV surge tester can test a Generator size roughly to 2500kW if 1200 rpm, larger kW for higher rpm.

The surge tester can also be used to do a DC hipot or megger of a conductor.

Always ground items under test while connecting and maintain one ground when testing.

Register to Reply
Anonymous Poster
#5

Re: Insulation Test Problem

10/16/2008 5:09 PM

Hi Ron,

You don't need an analogue meter you need one with a low impedance.

If you are indeed using a digital meter it will probably be 10MΩ input impedance if of high spec or 1MΩ if lower spec. You can always shunt down this voltage with a resistor of say 10kΩ. If this is just capacitive or inductive coupling then it will drop it to millivolts.

However why not use your Megger? You will be using 500V or 1kV so 7.5V will not do it any harm.

If I understand your question correctly you are testing the cable between your main switch room and the machine's isolator. If so, where have you been measuring the currents recorded?

Regards

Chas

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#6
In reply to #5

Re: Insulation Test Problem

10/18/2008 12:18 AM

Hi Chas,

Thank you for the advice;

1. Yes, I used a digital multimeter with an input impedance of 10MΩ, 30pF nominal.

2. The cable tested is from the Main Switch Room Circuit Breaker [Email-Westinghouse, Series C, 400Amp max., 600Vac, cat. KD3400F]to the Machine Isolator.

3. The voltage and currents recorded were similar when measured from:

(a) Isolator Line Side.

(b) Main Circuit Breaker Load Side.

4. Thank you, I used the Megger at 500Vdc and 1000Vdc, and all went well as you advised, "However why not use your Megger? You will be using 500V or 1kV so 7.5V will not do it any harm",.

Cheers!

__________________
Kind regards, Ron
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); dadw5boys (1); Ron Nombri (2); Switchman (1)

Previous in Forum: Partial Discharge Detection   Next in Forum: Load Calculation for 2-phase and 3-phase equipment

Advertisement