After isolating one of our machines from the main switch room, then from the machine's isolator, a pre voltage and current check was done on the isolator line side before insulation test could be done on the main supply cable. The results are listed below as measured with a multimeter and clamp meter.
1. Line to Earth Test.
a. Line 1 (Red Phase) - Earth Volts = 0.50V
b. Line 2 (White Phase) - Earth Volts = 3.960V
c. Line 3 (Blue Phase) - Earth Volts = 3.50V
Line to neutral test had similar results.
2. Line to Line Test.
a. L1 to L2 = 3.873V. b. L2 to L3 = 7.34V c. L3 to L1 = 3.429V
3. Current Test.
a. L1 = 0.17A. b.L2 = 0.42A. c. L3 = 0.25A.
4. Questions.
Is it safe to carry on with insulation test at the presence of these leakage parameters?
Because of the presence of voltage and current at the line side of the isolator, insulation test of 1000Vdc and 500Vdc was not done. I though in case it would have a bad feedback on the insulation tester and may damage it.
What are the standards (AS/NZS, British, others) regulating the minimum control of leakage voltages and currents after isolation?
Your assistance and advice would be great.
Thank you and kind regards,
Ron