Load Calculation for 2-phase and 3-phase equipment

10/14/2008 10:20 AM

I am trying to estimate electrical load (kVA) from a panel schedule for lighting, devices and equipment (The purpose is to help allocate costs between landlord and tenant for the electrical system).

I would like to know the basic calculation for 3-phase and 2-phase equipment.

For 3-phase equipment (such as an RTU), do I muliply voltage x amperage x sqrt. 3 x 3(since there are three breaker poles being used). For 2-phase devices (such as a receptacle for a welding machine) do I multiply voltage x amperage x 2(since there are two breaker poles used).

I know there may be a power factor involved in the calculation but I am ignoring that since I don't know it, and also I am aware I have to divide VA by 1000 to get kVA. Also my panels are 120/208V in case that information is important.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Load Calculation for 2-phase and 3-phase equipment

10/14/2008 11:37 AM

1- P (3phase)=3Vph x Iph x PF=1.73Vl x Iph x PF

2- P(1phase)=Vph x Iph x PF

--------------------------------------

Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#2

Re: Load Calculation for 2-phase and 3-phase equipment

10/14/2008 11:54 AM

Hi Guest;

1. 3 Phase Apparent Power "S" (VA) = 3 x V phase x I phase = sqrt. 3 x V line x I line

2. 2 Phase Apparent Power "S" (VA) = 2 x V phase x I phase

Phase wise, its 3 single phases and 2 single phases.

Phase voltage is voltage between one phase and neutral.

Line voltage is voltage between one line and another (with respect to the other line).

__________________
Kind regards, Ron
Reply
Power-User

Join Date: Jun 2008
Posts: 146
#3
In reply to #2

Re: Load Calculation for 2-phase and 3-phase equipment

10/15/2008 3:05 AM

You have to consider the power factor for a 3 phase calculation. If you don't know the power factor then a good ball park figure to use is 0.6.

Reply
Power-User
Engineering Fields - Electrical Engineering - Ron Nombri Engineering Fields - Energy Engineering - Ron Nombri Engineering Fields - Power Engineering - Eternal Power Papua New Guinea - Member - Ron Nombri

Join Date: May 2007
Location: Papua New Guinea
Posts: 174
Good Answers: 3
#4
In reply to #3

Re: Load Calculation for 2-phase and 3-phase equipment

10/15/2008 7:45 AM

Hi Andy,

Yes power factor must be considered for kW loading at that instant of voltage and current measurement.

For 3 phase system, P = sqrt. 3 x V line x I line X Cos(ø)

Where, Apparent Power "S" (VA) = sqrt. 3 x V line x I line.

As, Power (w) = S x P.F,

From which one can determine the kW loading and the kVA loading. Where, with some power utilities, the maximum billing on power is focused on the kVA. From which injecting reactive power, kVAR, will correct power factor reducing the kVA loading, and savings on money. This is applicable to large facilities and factories.

Anyway, cheers!

__________________
Kind regards, Ron