Modbus Comms Highway

10/16/2008 10:21 AM

Chemical engineer trying to wire up an additional device into a Modbus network. I am running a DeltaV DCS v. 7.3 and have an existing serial port card that has an existing GC communicating by 485 to the card. The card is the Master while the GC is the slave. The facility is adding another GC and needs it to talk to the DCS via MODBUS. Assuming that I have enough licensing, I am planning on adding the new GC to the existing card on the same port as the existing GC.

My question is how do I wire the MODBUS network to work? My current plan is to daisy-chain the new GC onto the end of the old GC and duplicate any terminations/end resistors needed on the new GC. Then I will call the new GC device 2 and set it up on the existing card. Does this sound workable?

__________________
Money doesn't talk, it screams in your face.
Register to Reply
Pathfinder Tags: Modbus
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Anonymous Poster
#1

Re: Modbus Comms Highway

10/16/2008 11:23 PM

For RS485 you need to wire the devices in parallel. That is make the same connections to each slave device. Usually the RS485 will be 2-wire so you need to connect A, B and GND to both of the GC's in parallel.

Don't duplicate the termination resistor! Move it so it's at the end of the cable (the last GC). The idea of the resistor is to avoid reflections from the end of the cable, that's where it belongs. Some MODBUS slaves have the termination resistor internal to the unit, you may have to set a switch or jumper to connect it in.

Hopefully you can copy the baudrate, parity and stop bits from the old GC onto the new GC. If not, for MODBUS normally 7 data bits, 1 stop bit and even parity are used. 9600 baud is common.

Register to Reply Good Answer (Score 2)
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#2
In reply to #1

Re: Modbus Comms Highway

10/20/2008 9:50 AM

Thank you for the advice, I will let you know how it turns out.

__________________
Money doesn't talk, it screams in your face.
Register to Reply