Sizing a Distribution Board (Consumer Unit)

10/17/2008 12:35 PM

My Dear Colleagues,

I want to size a Distribution Board (Consumer Unit). My total load is 50.2KW comprising A/C units, Lighting points, Pumping machines and other loads that will be taking source from 13A wall outlets.

Below is how I did the calculation for the rating of the main MCB of the DB,

I = 50.2 x 1000/1.73x400x0.8(Pf) = 90.8A

with 20% tolerance, = 1.2x90.8 = 108.96A

I therefore wanted to use 110A MCB and some combinations of 32A, 16A, 10A, 6A for distribution.

Please criticise and advice. Also shed more light on how to select the maximum number of breakers for distribution.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Oct 2008
Location: Ohio
Posts: 19
Good Answers: 3
#1

Re: Sizing a Distribution Board (Consumer Unit)

10/17/2008 3:19 PM

Posters should start to be much more specific on what juristiction they are operating in, and what rules they are operating under. For example, this type of sizing exercise, for most of the United States would be done per the National Electical Code, which provides some relatively clear guidance.

My guess, based on a few of your terms used, and clues like 13A wall outlets (in the US we would never use 13 ampere wall outlets, they are unlucky), is that you are not in the US, and not looking for sizing help that is NEC based.

Reply
Guru
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member

Join Date: Jul 2007
Location: FL Space Coast
Posts: 536
Good Answers: 14
#4
In reply to #1

Re: Sizing a Distribution Board (Consumer Unit)

10/20/2008 6:43 AM

Judging by the useage of the term "consumer unit" and 13A sockets, I would quess that he is in BS1362 land. Either Great Britain or one of their influenced former colonies. So I would guess that British standards apply.

Reply Score 1 for Good Answer
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#5
In reply to #4

Re: Sizing a Distribution Board (Consumer Unit)

10/21/2008 6:29 AM

Yeah, am from one of the British former colonies. So i use the BS....

__________________
One good Thing deserves Another
Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#2

Re: Sizing a Distribution Board (Consumer Unit)

10/18/2008 1:33 AM

Dear Colleque,

The incomer rating of the distribution board depends on the total load connected to the distribution board.The calculation done by you is correct.Hoewver you may take diversity factor(DF) of load usually around 69-80% of connected total loads.In this case taking Df as 80% , the total load on the incomer works out to 0.8 x 90.8=72.64A.Taking for future expansion of loads say 10%(if required), the incomer rating works out to 79.90A.Take the nearest standard available rating of MCCB shall be 100A. The no of out going feeder MCCB will depend upon number of out going feeders if you consider that each load will be fed by independent MCCB.The rating of each out going feeder MCCB depends upon the load of that feeder.Calculate the load current required for each out going feeder.Select the standard circuit breaker with rating higher than the calculated feeder rating.

__________________
Best Regards
Reply
Anonymous Poster
#3

Re: Sizing a Distribution Board (Consumer Unit)

10/19/2008 5:59 AM

you are in calculating your main breaker, i 100% agreed with you.. you can use 100A MCCB rating.. actually the function for the main breaker is to protect the whole panel from any faults and not from the individual connection.. this 100A amp is morethan enough even for the future expansion as what because of the diversity factor or demmand factor.. but for selecting the branches.. its the other issue.. for the motor calculate it according to its rating and just multiply it 150% for its starting current.. and if you make spare.. in my own idea as an contractor engr. dont use 10A or 6A.. use 15A or 20A as standard.. coz ussually we use 4mm² wire or 10AWG which carries morethan 20A current...

Reply
Participant

Join Date: Sep 2007
Posts: 2
#6

Re: Sizing a Distribution Board (Consumer Unit)

03/01/2009 7:57 PM

I = 50.2 x 1000/1.73x400x0.8(Pf) = 90.8A

hi, im new at this. What is the name of this formula?

Reply
Participant

Join Date: Mar 2015
Posts: 1
#7
In reply to #6

Re: Sizing a Distribution Board (Consumer Unit)

03/24/2015 5:09 AM

P=Square Root of 3 * V * I * cos (the angle between KW&KVA)

cos (the angle between KW&KVA) = Power factor = p.f

and he use it to calculate the current to know the rating of the DB Incomer.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8

Re: Sizing a Distribution Board (Consumer Unit)

11/27/2023 3:51 AM

The outgoing breakers are there to protect the circuit wiring downstream. The circuit wiring size depends on a number of factors, including circuit length, permissible voltage drop, and method of installation of the cables.

Cable sizing has to take into account the permissible voltage drop en route to the load and the ability of the cable to survive a fault current safely until the breaker operates to disconnect it.

The best recommendation possible is to deploy the electrical standards applicable in the country of installation; in the UK, for example, British Standard 7671 applies.

If in doubt, as suggested by the original post, consult a local qualified Electrician, who will be more than capable of carrying out the calculations, installing the circuits, and testing and certifying it afterwards. Expect to receive an installation certificate document covering the work at handover.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); EnB (1); IanR (1); OscarOfWaldo (1); PWSlack (1); Qusai Alazzam (1); V.Ambarani. (1); vocalmind (1)

Previous in Forum: All metal Keyswitch with NO (Normally Open) contact block   Next in Forum: Alternator neutral groundig

Advertisement