Current carrying capacity of aluminium

10/19/2008 3:03 PM

I wanted to know the size reqd. aluminium flat for 840Amp current at 66KV level?

Register to Reply
Pathfinder Tags: current carrying capacity
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Current carrying capacity of aluminium

10/19/2008 7:17 PM
Register to Reply
Power-User

Join Date: Jan 2008
Location: since 20 Jan 09, the USSA
Posts: 375
Good Answers: 81
#2

Re: Current carrying capacity of aluminium

10/19/2008 11:24 PM

Not sure what you mean exactly by the term "flat." Assume this is one of those King's English terms that doesn't translate exactly across the Pond. But in general if you are using wire of any type to conduct electricity from one point to another, you have to have the following data in hand before you can answer your question fully. You need to know how much potential or tension drop or power loss you can stand, and you need to know how long the conductor will have to be. 840 Amps sounds more like busbar than wire, but the principle is the same. The equation that governs this is R= pl/A, where R is resistance in Ohms, and I have used p for the Greek symbol rho, which is the resistivity of the material in question in Ohm-cm or Ohm-meters, l is the conductor length in cm or meters and A is the cross-sectional diameter in sq cm or sq meters. The cross-sectional area is of course related to the wire gauge you are looking for, and the resistance term is the allowable potential or tension drop across the length of the conductor divided by the amperage to be carried. Once you have this data, you can look up the wire gauge in a table, as suggested by the other respondent. My old 1953 Reference Handbook for Radio Engineers even has a table of required wire gauge for various amperages and lengths of conductor based on 2% voltage drop. But it's for copper wire - I believe gauges are different for aluminum.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Current carrying capacity of aluminium

10/20/2008 7:59 AM

Sizing conductors be they wire or bus bar is not the simple exercise most people believe it to be. You need additional information. Length is needed to determine voltage drop. Ambient temperature is needed, Is the structure outside? How much solar heating is expected? Latitude? How about cooling? Is it to be forced air cooled? Is it located in a windy environment? Is is buried? Is it inside housing? What color? The design of these is best left to personnel or companies with experience in their design. We have had good performance from Powell Electrical Systems Inc. at www.powellind.com

Register to Reply
Anonymous Poster
#4

Re: Current carrying capacity of aluminium

10/26/2008 5:48 AM

you can use 12.5mm x 112.5 mm size of alumnium busbar subject to the ambient temp is not more than 50 and working tem is not more than 60 degree c.

Register to Reply
Participant

Join Date: Dec 2006
Posts: 3
#5

Re: Current carrying capacity of aluminium

10/27/2008 10:40 PM

For preliminary calculations current density for aluminium bus bar ≈120A/cm2

Cross sectional area = 840/120=7cm2 accordingly size may be arrived from mfg catalouges

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); emc_c (1); kasinikota srinivasarao (1); wareagle (1)

Previous in Forum: Shortcircuit current   Next in Forum: Lux level calculation

Advertisement