Voltage Drop Details

10/21/2008 9:30 AM

Dear Sir,

What is the allowabel % voltage drop for 11 KV XLPE Aluminium cables as per IEEE or BIS Standard. Kindly give the details sir.

Thank you.

Regards,

T.Kailash Kumar

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Voltage drop details

10/21/2008 10:08 AM

British Standard 7671. Again.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6
In reply to #1

Re: Voltage drop details

10/25/2008 4:55 PM

Is the British Standard 767 similar to the US NEC? Does it dictate a max VD?

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Voltage drop details

10/21/2008 10:22 AM

Cable does not have an allowable % VD. You must determine what is the max VD you can tolerate. The NEC Std suggests 3% but not mandatory. It is a design problem.

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#3

Re: Voltage Drop Details

10/22/2008 12:24 AM

The allowable voltage drop depends upon how the electrical power distribution system has been designed and the capability of the electrical loads to function suitably at the reduced voltage at the terminals of the electrical equipment. In case of motor loads you also need to take into account the voltage drop occuring diuring the starting time. Voltage drop for sizing of cables is mostly applicable for voltages upto 1000V. As a general rule for volatge levels of 3.3kV, 5kV, 6.5kV and higher it is the fault current carrying capability that plays a major role.

The standards refered by you do not define a certain % voltage drop for a cable.

__________________
Atlas Shrugged - JGD
Register to Reply
Anonymous Poster
#4

Re: Voltage Drop Details

10/22/2008 8:19 AM

How long is a piece of string?

Register to Reply
Associate

Join Date: Aug 2008
Posts: 39
#5
In reply to #4

Re: Voltage Drop Details

10/23/2008 12:21 AM

Dear sir,

It is approximately 500mts

Thank you.

Regarda,

T.Kailash Kumar

Register to Reply