Selection procedure of Lightening Arrestor

10/22/2008 2:28 AM

What is the best method to choose accurate level of voltage co-ordination of Lightening Arrestor for 132 Kv system voltage and provide detailed calculation for selection of the same.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Selection procedure of Lightening Arrestor

10/22/2008 3:19 AM

Dear Sir,

You can provide 120 kV Lightning Arrestor for 132 kV System.

Best Wishes,

N.Suresh

Register to Reply
Participant

Join Date: Dec 2006
Posts: 3
#2

Re: Selection procedure of Lightening Arrestor

10/27/2008 10:08 PM

very simple, Rating of LA is √2/√3(Highest system voltage) for example Highest system voltage of 132 kv generally as per code 145 kv now u calculate √2/√3(145) gives u the LA Ratings is 118.39 KV as a standard size it should be 120KV LA.

Register to Reply