Copper Bus Bar Selection

10/11/2006 4:21 AM

What is the crieteria for selecting Copper Bus Bars for current load and the calculation method of arrving at the sizes of these bars for ones requirement?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Oct 2006
Location: Hyderabad,India
Posts: 49
#1

Re: Copper Bus Bar Selection

10/11/2006 5:51 AM

Dear sir There is a paraallel in sizing the copper bus bars with that of cable sizing.Both are similar. 1)Current carrying capacity.(load current) 2)Heat dissipation. 3)mutual inductance effects (interleaving of bus bars(for higher currents)). I have heard of Thomas Rata method for bus bar size calculations. regards Ravipra01

Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#2

Re: Copper Bus Bar Selection

10/13/2006 2:26 PM

You raise a complex question.

*Bus Bars are generally sized to limit heating at rated
load to an acceptible level under prevailing conditions.

*Mechanical strength to resist magnetic stress under
available short circuit conditions are a factor.

*Sometimes 'current limiting` orientations are selected.

Safety margins are applied, some are mandated, others discretionary.
Limits depend on the appplication.

Reply
Anonymous Poster
#3

Re: Copper Bus Bar Selection

02/12/2009 6:22 AM

I want Copper Busbar selection Calculation

Reply