kvar
10/26/2008 1:54 PM
how to calculate kvar,what is this
Re: kvar
10/26/2008 6:33 PM
You must know the load in kw and the power factor.
KVA = kw/pf. KVAR = sqrt(KVA² - KW²)
Engineering Fields - Power Engineering - Projects Engineer
Re: kvar
10/28/2008 9:34 AM
Kvar is the reactive component of the AC inductive circuit,i.e the lower the power factor the higher the Kvar and vice versa.
KVA X cos.= KW ( usefull power )
KVA X Sin = Kvar ( Reactive . useless power)
We try to maintain higher PF(lower kvar) to improve power utilization efficiency
e.g at 50% PF the efficiency of power utilization is 50 % the rest is reactive(kvar) but the consumer will pay for 100%