Electrical Distribution and Power System Construction

10/27/2008 2:57 AM

1.In standard practice,is it possible to install rated 50 hz inductive loads in a rated 60 hz power supply or vise versa?

2. Does it affects the performance of the equipments and the power supply?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Interested in everything- see my Profile please APIX Pilot Plant Design Project - Member - Member Engineering Fields - Electrical Engineering - Member Engineering Fields - Power Engineering - Member Engineering Fields - Civil Engineering - Member Hobbies - Musician - Autoharp and Harmonica Hobbies - Hunting - Member Hobbies - Fishing - Member

Join Date: Nov 2007
Location: Christchurch, (The Garden City), South Island, New Zealand
Posts: 4395
Good Answers: 230
#1

Re: electrical distribution and power sytem construction

10/27/2008 4:16 AM

Hello kylyn

1. Yes.

2. Yes.

It is not generally regarded as advisable to cross-install electrical equipment, because performance will suffer, along with longevity of the equipment.

There is another reason: 50Hz and 60Hz equipment generally have different voltage supply requirements.

Kind Regards....

__________________
"The number of inventions increases faster than the need for them at the time" - SparkY
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#2

Re: Electrical Distribution and Power System Construction

10/29/2008 9:31 AM

Yes provided voltage and power rating are same.

Definitely.A 50Hz inductor will have a higher reactance and there higher impedance when installed in a 60HZ circuit and vice versa.Performance there fore suffers

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#3

Re: Electrical Distribution and Power System Construction

11/01/2008 4:50 AM

what you should be aware of is that inductive equipment rated for 60Hz will have a lower reactance at 50Hz and so will draw more current at that frequency. This often leads to overheating and earlier failure. In the case of motors this problem is exacerbated by the fact that the motor and therefore it's cooling fan also will be running slower and thus providing less cooling.

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#4

Re: Electrical Distribution and Power System Construction

11/04/2008 12:30 AM

XL= 2.∏.f.L

if f= 50 Hz, XL = 2.∏.50.L = 100.∏.L

f= 60 Hz, XL = 2.∏.60.L = 120.∏.L

in motor, if XL become higher , then current become higher too.

P = I².Z.cos Φ

P = I².(R+jXL).cos Φ

Z is impedance per phase---> so if XL increase, it cause P increase too

Register to Reply
Anonymous Poster
#5

Re: Electrical Distribution and Power System Construction

11/08/2008 7:27 AM
Dera Friend,

You can operate the 50 hz m/c on 60 hz system, provided m/c is not over loaded.

the effects are -when 50 hz m/c connected to 60 hz system, magnetic saturation may take & magnetic losses increases, over heating the equipment. So, you may have to reduce the operating load. Further, with 60hz, speed of m/c shall increase by 20% and your drive should have speed controller to match with your geared system.

On connecting 60hz m/c on 50 hz system, m/c shall work with 20% lower speed, & lower torque. Further, Voltage need to be reduced propertionately to keep v/f ratio constant, to maintain torque. The system shall be more efficient. for this, vfd drives are available.

If 50hz transformer is connected to 60 hz system, equipment will be over heated. but 60hz transformer shall work cool on 50 hz system.

regards.

Register to Reply
Anonymous Poster
#6

Re: Electrical Distribution and Power System Construction

11/12/2008 4:15 PM

Hey we sell this stuff check us out, email us with ANY questions.

http://connect2-4less.com


Marty

Register to Reply