Is it healthy to maintain the rated current for motor during running condition??

10/27/2008 11:16 PM

I have a 45kW induction motor(air cooled) which drives an exhaust fan, its rated amp=74A. Our current reading is at 73A, motor caging temp=80degc. Is this normal?

Now if the rated amp of a motor is 74, what should be my current reading having a 75% load.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Is it healthy to maintain the rated current for motor during running condition??

10/27/2008 11:29 PM

Dear,

Temperature and current both are not normal.

Check out both quantities reponse during no load condition.

Kind regards,

Register to Reply
Member

Join Date: Oct 2008
Posts: 6
#2

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 12:23 AM

no load amp = 28.1A at 48degC caging temp.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#3
In reply to #2

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 1:00 AM

The body temperature of motor should not be above ambient temp by 40 deg C.

I would suggest reducing the load by throttling the damper ( if present)

cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Member

Join Date: Oct 2008
Posts: 6
#4

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 1:25 AM

originally, its damper (suction side only) is throttled at 75% opening, but since we had installed a vfd for it, we opened it to 100% and reduced speed of fan to obtain the required suction. But still, at 50Hz, 440VAC, the current drawn by the motor is at 69.43A and the temp of caging is at 80 degC.

It causes frequent breakdown on our VFD and affects our process..

maybe there is someone who could help me on this one.

Thanks a lot. Your response are highly appreciated.

Register to Reply
Power-User

Join Date: Aug 2008
Location: East
Posts: 117
Good Answers: 6
#5
In reply to #4

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 7:16 AM

Is the motor designed to run at lower speed through the use of a VFD. If not then its temperature will rise above the one observed during running under normal load as its heat dissipation largely depends on the air draft being circulated through it because of the motor rotation.

You may have to change your motor or try to install an additional fan apart from the shaft mounted fan on the motor.

Does the VFD trip because of sensing of higher temperature of motor.

__________________
Atlas Shrugged - JGD
Register to Reply
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#7
In reply to #4

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 10:00 AM

have you checked the vfd program ,settings ,why did you go for vfd ? what was the original start/run equipment.

maybe the motor is not suitable to run at lower speed ?

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#8
In reply to #4

Re: Is it healthy to maintain the rated current for motor during running condition??

10/29/2008 10:33 AM

I would suggest checking the parameters at VFD .

What is your VFD rating ? I always suggest to install VFD one size bigger than the motor size ( If motor is 30 Hp, i install VFD of 40 hp)

The drive manfacturers have lot derating factors ( normally writen in fineprint...) like ambient temperature, altitude etc.

Is your motor inverter duty rated?

cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6

Re: Is it healthy to maintain the rated current for motor during running condition??

10/28/2008 9:15 AM

Also check to see if your motor has accumulated a lot of dust. Air flow and a clean motor are very important near full load.

What is the air temperature near and around the motor?

Everything (including insulation) degrades faster at elevated temperatures.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#9

Re: Is it healthy to maintain the rated current for motor during running condition??

10/29/2008 12:43 PM

You have probably already checked this but,

1) Is the overheating there without the VFD? Is this the same motor that has always been there? You can expect some extra heat just from the nonsinusoidal output of the inverter, but nothing that will eventually peel the paint. If the motor runs normally without the VFD, guess where the problem is.

Check to make sure the windings of the motor are connected correctly. Sometimes in a multiwinding motor, when the configuration is delta, if the unused delta windings are not open induced voltages in this winding will cause overheating.

This sounds like a european application from the kW rating you mentioned. Was there a star-delta starter before the VFD installation? Make sure the VFD is configured correctly for the motor.

That is about all I can think of at the moment

Register to Reply
Member

Join Date: Oct 2008
Posts: 6
#10

Re: Is it healthy to maintain the rated current for motor during running condition??

10/30/2008 8:52 PM

Thanks guys, i appreciate all your inputs.

Even without the VFD, the values that i had mentioned at the top of this topic had been seen.

Wye-delta start is in parallel with the VFD but not simultaneous, in case of VFD failure we switch from VFD to direct line connection.

We also changed the motor with the same capacity, but i still get the same result.

We already checked the parameters and all parameters are ok.

Is it possible to size up the capacity of the motor while retaining the existing VFD.

Register to Reply
Anonymous Poster
#11
In reply to #10

Re: Is it healthy to maintain the rated current for motor during running condition??

10/31/2008 12:56 PM

The motor sounds hot and if the current is near full load but the applied load is much less it means you are applying too much (overfluxing or 'pushing current')or too little voltage (partial stalling)at the reduced frequency.

If no load is 28A and full load is 74A for the motor then 75% is about 65A.

You do not mention the rated motor voltage / Hz and also your mains supply voltage.

Some VFDs scale the output by input supply, others are definitive voltages.

If the motor is 440V/3ph/60Hz then 5/6 of this voltage would be OK at 50Hz output (i.e.365V at 50Hz)simplistically

If you have a 460V mains and the inverter is outputting 5/6 you may be overvolting which would explain your first postion when D-o-L.

If so, find out how to set the VFD scaling of v/f to get a better result.

Register to Reply