What is the recommended material of hardware (nuts & bolts) used for electrical cable connection? Is plated steel hardware OK or we shall use Copper or brass? One of our Customers is asking us to supply copper or brass hardware for connection between earthing cable (which is copper) and brass earth strip in distribution board. What are the factors governing this selecation?

__________________
Rajesh
Register to Reply
Pathfinder Tags: cable connection hardware
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#1

Re: Cable connection hardware

10/28/2008 10:24 AM

You need to be careful of reactions between dissimular metals! ie, if you have copper strap and a steel terminal, an electrolytic reaction will occur if any moisture is present thus erroding the connection! This is why it is always best to use the same material or a bi-metal connector when joining the straps to other materials!

Check this out!

Hope this helps.

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Commentator
Australia - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jan 2008
Location: Mount Gambier, South Australia
Posts: 56
#2

Re: Cable connection hardware

10/28/2008 11:38 PM

It does depend on where and what you are doing. On the large LV/MV switchboards we have worked on we would use plated steel uts, bolts and washers, and sometimes use a corrosion inhibiting paste. If you are using copper lugs bolted to a copper busbar then the current flow is between the two faces and generally not the bolt. With earth bars and terminations, if we where using 6mm (or 1/4") or larger bolts then plated was fine.

Regards,

Trevor.

__________________
tooz
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Cable connection hardware

11/03/2008 8:50 AM

Don't use copper or brass in saline atmospheres. They don't last long...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Mr. Truman Brain (1); PWSlack (1); tooz (1)

Previous in Forum: Is it healthy to maintain the rated current for motor during running condition??   Next in Forum: RS View32
You might be interested in: Copper, Brass and Bronze Alloys

Advertisement