Previous in Forum: UPS   Next in Forum: how much motor power is needed to run a vehicle of 300kgs (incl vehicle weight)
capacitor bank use for pf
10/28/2008 1:51 PM
how to check capacitor bank condition
we have 430kvar capacitor panel(total 8 bank,eatch bank 86.6amp,60kvar),mature the current following--
capacitor bank no-01 -R PHES 28AMP, Y PHESE36AMP,B PHESE 45AMP,
,CAPACITOR BANK 02- R phase 42amp, Yphase70amp,Bphase42amp,
tranformer-1500kva
load-800amp
pf-0.9 r,y,b
pls give me good anwer-this capacitor bank good condition or---------
Good Answers: 40
Re: capacitor bank use for pf
10/28/2008 2:05 PM
The way we used to check large capacitor banks in our transmitter unit, was to time its discharge cycle through a large wire wound resistor of known resistance. This would give us the RC time constant and thus its capacitance.
Engineering Fields - Power Engineering - Projects Engineer
10/29/2008 2:42 AM
By rule of thumb current measurement(to the capacitor) is a good indication of the condition of the capacitors ,IF all the phases have the same inductive load than the current flow will be the same.
reliable way is to use a capacitor meter to measure tha capacitance of each of the capacitor,the reading should be withine +/- 10% of the name plate.
But if your PF is being maintained by the Caps ,you only need to regularly take the current readings and record in a log book,this will give you a good history to refer when in doubt.
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer