We have a trailer mounted aircon supplying conditioned air for aircrafts. The compressors and motors are run by a generator(480V AC, 60 Hz, 3Φ). The evaporator motor is rated at 60HP and drives an impeller type fan made of steel (OD = 26.5in.) and weighs about 25kg (55lbs). The motor's normal running current is 80Amps as per motor's nameplate. However, when we run the unit, the evaporator motor's running current is at 90Amps which is above the motor's protection limit of 85Amps. We checked the motor's insulation and found it to be good.- it is a new motor, btw.
We had recently taken the old motor out because of the same problem, after we changed bearings and re-insulated the motor. The old motor's insulation was good but the running current was also at 90 Amps, thus we changed motor. We cannot adjust the over current protection switch as 85Amps is the manufacturer's recommendation.
Can anyone help me out here? Need to know what's causing the high motor current and how to correct it. Or should I adjust the overcurrent protection switch to 95Amps?