Electric Motor Problem

10/29/2008 7:59 AM

We have a trailer mounted aircon supplying conditioned air for aircrafts. The compressors and motors are run by a generator(480V AC, 60 Hz, 3Φ). The evaporator motor is rated at 60HP and drives an impeller type fan made of steel (OD = 26.5in.) and weighs about 25kg (55lbs). The motor's normal running current is 80Amps as per motor's nameplate. However, when we run the unit, the evaporator motor's running current is at 90Amps which is above the motor's protection limit of 85Amps. We checked the motor's insulation and found it to be good.- it is a new motor, btw.

We had recently taken the old motor out because of the same problem, after we changed bearings and re-insulated the motor. The old motor's insulation was good but the running current was also at 90 Amps, thus we changed motor. We cannot adjust the over current protection switch as 85Amps is the manufacturer's recommendation.

Can anyone help me out here? Need to know what's causing the high motor current and how to correct it. Or should I adjust the overcurrent protection switch to 95Amps?

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#1

Re: Electric Motor Problem

10/29/2008 9:16 AM

Please First check the class of Insulation .It should be Class F or some times it could be class B.Take the temperature rise.Including ambient it should be within 120Deg for class B and 145 For class F.That is if your ambient is 40Deg rise can be 80Deg C.If temp. is within limits motor is safe.Now as regards current the motor may be overloaded due to incresed fan out put .The other reason is you need to check the Torque speed Curve of fan with that of motor and get the duty point which will enable u to determine what current it should draw.What is the rated rpm ,Frame size of motor.Also whether u have a service factor rating if so what is it?If u can give the same may be further clarification can be given.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#2

Re: Electric Motor Problem

10/29/2008 10:22 AM

Hello Maintenance Man,

My first line of thought would be the generator rpm > Frequency.( Are you running at 60.5 HZ?)

The Fan rpm ( which in turn is decided by frequency of power supply) has direct influence on current drawn.

Check the Hz and do not exceed 60Hz. You may even reduce it to 59.8 Hz by reducing the engine speed and check the current.( Ensure the voltage is 480volts)

Cheers.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#3

Re: Electric Motor Problem

10/29/2008 8:33 PM

Has anything changed?--I take it that this was a running system at one time.

Healthy motors can draw unhealthy amps on air movers if the amount of intake air isn't under control--at least this is something I have had to deal with. Has anything changed in how the air enters the fan? Or is there a restriction on the air leaving it?

If there is anyway to restrict the air to the fan, I would and watch the amp draw and get it to where it needs to be and see if it will run normally there.

I would abandon suspecting the motor anyway. Try to restrict the air to it.

Best of luck!

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2007
Location: Somewhere in the hills of Pennsylvania, I think.
Posts: 246
Good Answers: 4
#4
In reply to #3

Re: Electric Motor Problem

10/29/2008 10:42 PM

Very good point to restrict the intake to reduce the current draw. I don't think that the manufacturer of the equipment would have designed a system to work in an overloaded condition or to take advantage of the SF rating of the motor. Too much money involved should there be a warranty claim due to a burned up motor. I don't know what happened to cause the increased current but looking for something that is missing in the intake or exhaust path is a good start. The more air moved, the higher the current draw. That's my 2 cents.

__________________
I'm somewhere between the age of thirty-something and Alzheimer's. I just can't remember where!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#10
In reply to #3

Re: Electric Motor Problem

10/30/2008 12:11 PM

I think you are on the right track. If possible get the mfg specs as to air flow and adjust the air flow to match. I, too, think high air flow is the problem if the gen set and motor is not showing a specific problem. If lowering the air flow causes low output temps, check to refrigeration system. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Member

Join Date: Oct 2008
Posts: 5
#5

Re: Electric Motor Problem

10/30/2008 12:48 AM

Check the alignment of the motor drive shaft and its connection and test run first the motor with no load see to it what amps been registered it should be only at 5-10 amps with no load, as you have told that the current rating is only with max of 80 amps with load, and make sure that the fan is been dynamically balance as you have said the motor is new so the problem goes all the way to the driven part of the equipment and make sure that its free from any distortion of vibration, it can cause high amperage registration.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#6

Re: Electric Motor Problem

10/30/2008 7:33 AM

A couple of things yu could look at.

Generator out put is one, however usually higher-cleaner voltage will reduce amperage.

Air flow, the suggesin about restriction is good but usually I have found the drive pulley or driven sheave has been replaced by a person who thought "what the heck it's only a Half inch bigger" resulting in an increace of a 1" of static thuss raising your amperage into the service factor of the motor.

Call the manufacturer of the equipment to see what the recommended Sheave and Pulley sizes should be. Or get something the same size and install adjustable variable pitch drive pullies. Open the pulley and reduce the RPM reducing the load and Amperage. Use a clamp on meter to check amperage after each adjustment is complete.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Participant

Join Date: Apr 2008
Posts: 2
#7

Re: Electric Motor Problem

10/30/2008 9:04 AM

First I would check the output voltage from the generator when the motor is running to make sure it is at the proper voltage, Check the frequency of the output from the generator. I am not sure if the generator was original to the setup or not, Dependent on the generator size it may not have the capacity to start and run motors, Most of the time generators need to be over sized for motor loads.

Register to Reply
Anonymous Poster
#8

Re: Electric Motor Problem

10/30/2008 9:44 AM

Little known fact, but gens need to be run regularly to maintain the "conditioning" of the electromagnetic components. If your system was stored for a time then you may have a gen problem that is causing low output and high draw on the motor.

Different problem but another road to check out is if the compressor motor is causing feedback into the fan motor gen system.

Air path others have mentioned. pressure wash the coils and fan, that kind of thing.

Best of luck to you, sounds like you have done a good job of checking things out and fixing em up so far, but your problem and system seem kind of tricky.

Register to Reply
Commentator

Join Date: Jun 2008
Posts: 80
Good Answers: 5
#9

Re: Electric Motor Problem

10/30/2008 11:46 AM

Is there a service factor listed on the nameplate? You are probably aware of this, any 40 deg C motor is suitable for continuous operation at rated load under normal conditions. When voltage and frequency are maintained at nameplate values, the motor may be overloaded up to the HP obtained by mutiplying the rated HP by the service factor shown on the nameplate. There might be a different temperature rise, efficiency, power factor , etc. but the motor is not supposed to sustain damage at these conditions. You are at 1.125 times rated now, if the motor is rated at 1.15, which I suspect it is, operation should be OK.

That's the ignore it solution, option 2 is one that will reduce amps.

Option 2 is to reduce the fan diameter, This will require procurement of a smaller diameter fan rotating element. I did some quick calculations and if you reduce the fan diameter by 1/2" amps should drop by 5 and a diameter reduction of 1" should reduce amps by 10. Remember power is a cubic function. Was there a blade replacement in the past history of the unit? We had someone procure a replacement fan rotating element with the only critera being shaft diameter. Of course the new one was larger and we tripped on overload. The motor does not know what it is connected to, it will run, or try to run at the system requirements. It is possible to "run-out" a fan and damage the motor so be careful of the changes you make. Call the vendor and make sure your dimensions are correct, or compare to another unit if available.

I hope this helps

Register to Reply
Anonymous Poster
#11

Re: Electric Motor Problem

10/30/2008 3:25 PM

I'm not exactly sure what you unit is, but a couple of suggestions come to mind. First is your voltage low which would drive up the current.

Secondly, if the fan is not direct driven. Ck to make sure proper alignment and drive belts not overtight.

Third, there should be a fan curve that depicts HP/static/flow/ect. for the fan. Not all, but some types will require additional HP, (i.e. current) if there is insufficient static (i.e. reistance) on the fan. I haven't ck'd rated current for the motor but it doesn't sound like your too far over. There haven't been any modifications, such as filter or shrouds removed? Condensors that are "more open", that type of thing? Easy test just to block off or restrict a good portion of the discharge air and see if the current drops.

Register to Reply
Power-User

Join Date: Jan 2007
Location: Houston,Texas
Posts: 378
Good Answers: 24
#12

Re: Electric Motor Problem

10/30/2008 3:32 PM

Fan Motor current draw will be a cubic function of RPM, (RPM3), a quadratic function of pressure (P2), and a linear function of SCFM. However, if the generator speed is say 63Hz (5% overspeed) , amperage draw of the fan motor will be 115.8% of full load, or92.5 Amps. A 4% overspeed of the generator to 62.4 HZ would result in the current readings you report --assuming that 60.0 HZ results in 100% (80 AMPS) fan motor loading. An speed error of 3-4% is very possible if the generator meter has not been calibrated recently or the governor is misadjusted.

__________________
Keith E Bowers, PMP
Register to Reply
Power-User
Hobbies - HAM Radio - New Member United States - Member - New Member Hobbies - Hunting - New Member

Join Date: Jun 2008
Posts: 440
Good Answers: 7
#13

Re: Electric Motor Problem

10/30/2008 7:12 PM

One simple thing--He is having problems with only one motor.

It's sounds like there are possibly four or more motors and no problems mentioned with any others.

If he went to all the trouble of replacing a motor without checking voltage after taking high amp readings--Not a chance--He is the Maintenance Man! and I have faith in him.

__________________
Those who believe in telekinetics, raise my hand --Kurt Vonnegut Jr.
Register to Reply
Anonymous Poster
#14

Re: Electric Motor Problem

10/30/2008 8:48 PM

Ok I will put my two cents worth also but as guest ....

It looks like there is more than one motor.... one would need to check the voltages at the problem motor and at least one other motor not just what is coming out of the generator , so far nobody has even hinted that a cable could be suspect in which case the voltage at the over current motor would be lower and of course the current would be higher than normal.... this is not to say the other suggestions are without merit hey even the new motor could be defective from the box it happens.

? Is the current 90A on all three phases or close like 87,91 93 Range and is the voltage at the generator right on 480V give or take 5% ?

Register to Reply
Register to Reply 14 comments

"Almost" Good Answers: