limit switches testing

11/03/2008 8:20 PM

We have limit switches 24V dc used for turning gear of the engines, how can it be tested for healthiness?

also the testing procedure for proximity type speed sensor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#1

Re: limit switches testing

11/03/2008 8:40 PM

If the switches are sealed snap action switches, the only practical test is resistance when the switch is closed.

__________________
Bob
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#2

Re: limit switches testing

11/05/2008 11:11 AM

The only way I know to test proximity type speed sensors is to monitor the output while the shaft/gear moves. If you are getting the expected output while the engine is running, you should get one that varies at a lower frequency while it is down and on the turning gear. If the machine is not running and not on the turning gear, the output of the prox amp is going to reflect the size of the gap between the prox and the gear. The voltage/current will be static but within a certain defined range if the machine is not turning. Usually there is an offset on the output of the prox amp which will allow you to do some diagnotstics based upon the voltage level of the output.

If the voltage out of the prox varies between, for example, -10 VDC and -12 VDC and you find the voltage less than -8 V or more than -14 V then you have a failure.

The only way to test the switch is I believe to exercise it to verify operation as was said above.

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
2
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#3

Re: limit switches testing

11/05/2008 12:55 PM

Before you grab your ohmmeter to measure contact resistance, consider this:

To determine the condition of the limit switch contacts you need to consider the level of current that the switch is to carry (more on this in a little bit). The fact that it is a "limit" switch indicates that it is a safety device of some kind. That being said, there are two possibilities for operating condition.

The first is one that requires "Normally Closed" contacts to be making a connection or the device will not run (commonly used on E-Stop circuits). If this is what you are using, then you will know if you have bad contact health by the fact that you have trouble starting or maintaining a normal run (i.e. frequent interruptions) condition.

If the contacts used are "Normally Open" they indicate a trigger device which is more likely to fail for mechanical reasons than electrical. Some people may scoff at this but it is true. Broken linkages, freedom of movement and missing lubrication are frequent causes but those things are not electrical.

Contact resistance is a field of its own. A standard analog or digital ohmmeter will give you different results depending on what scale you use. Most people do not appreciate how difficult it is to measure a low resistance value of less than one ohm. Special meters and techniques give better results. But more than that, it is important to take several readings and calculate an average result. It is also important to make sure that the pressure placed upon the switch is approximately the same for each reading. You will have to compensate for leadwire loss, etc. but the contact resistance of most appropriately selected switches should be fairly low.

I would expect an average contact resistance of up to 0.2 ohms to be good. An average contact resistance of up to 0.5 ohms to be fair. An average contact resistance of up to 0.9 ohms is beginning to be questionable. Above that, I would be looking for a replacement switch. If, however, your numbers are all over the place (i.e. a standard deviation > 0.4 ohms) then you should find another meter or test setup.

For circuits that pass more than 50 mAmps through the contacts, an ohm meter may give misleading results. In those cases you will need to set up a power source, a stable load and then measure the voltage across and the current through the contacts. Most Ohm meters are simply not designed to test impedance at higher current levels.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply Good Answer (Score 2)
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#4
In reply to #3

Re: limit switches testing

11/05/2008 1:59 PM

Excellent comments on the difficulty of determining the condition of the switch contacts.

In the answer I gave, I assumed that the switch would be tested under the same electrical and mechanical load conditions as it is normally used. That is not always a good assumption! I also agree that my suggestion did not monitor degradation of the contact state unitl it failed the test.

Thanks!

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#5
In reply to #3

Re: limit switches testing

11/05/2008 4:49 PM

GA.

__________________
Bob