describe the steps to calculate the ampere hour of a battery of 24 volt connected to a machine of input power 4 kw to operate for 2 hours

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#1

Re: load calculation

11/04/2008 8:55 AM

Hi Guest ,

Sorry I think this is not your class room and we are not your students to answer your question.

Regards

Reply Good Answer (Score 2)
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#2

Re: load calculation

11/04/2008 10:44 PM

describe yourself first !!! where do you live, what is your job ? etc...etc....

Reply
Anonymous Poster
#3

Re: load calculation

11/05/2008 12:52 AM

hang on guest, someone else may of more help...

Reply
2
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#4

Re: load calculation

11/05/2008 12:24 PM

The energy required is : P * t, where P = 4 kW (power) = 4000 W and t = 2 hr (time).

This energy has to be obtained from the battery. The energy delivered by the battery is U * I * t , where U = battery voltage = 24 V, and I*t is the battery capacity in Ah.

Since the battery shall be discharged only up to approx 70% of its capacity (keep 30% as reserve to avoid complete depletion), select a coefficient K = 0.7.

P * t = K * U * I *t

thus: I * t = (P * t)/(K * U), and, entering the values: (4000 * 2)/(0.7 * 24) = 476 Ah.

The capcity may be affected by losses in the connections conductors, etc,

__________________
Scientes et audaces fortuna juvat !
Reply Good Answer (Score 2)
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#5
In reply to #4

Re: load calculation

11/07/2008 4:05 PM

Good answer Tomad,

but two items need mentioning, firstly the question of Peukerts exponent.

We cannot go into the maths of this as we do not know what type of battery he is using. However the poster will need to take into account that if he wishes to discharge his batteries over 2 hours he will need to look for a battery rating marked at C2. The following is the data for a heavy duty 2V cell designed for such applications. As can be seen the quicker the discharge the lower the available capacity.

If the poster uses 12V monoblocs he will find that they are usually rated at C20 and so will appear to have an even higher rating. To compound this possible mis-specification monoblocs are rarely rated for 70% discharge and to discharge this type of battery so deeply will lead to a very short service life.

The question of losses in the cables and contacts is unlikly to have any great effect on the capacity calcs but it is quite possible that the actual load is at 120Vac or 230V ac and thus fed from an inverter. In which case losses of 8% to 15% should be factored into the calculation.

If the question is a related to an anticipated project i would advise the poster to ask advice from an experienced marine electrician or a fork lift truck maintenance company, both of whom are dealing with this sort of capacity and loadings on a regular basis.

Regards

Chas

7 OPzS 490 = battery type

490Ah = Nominal Capacity

546 = C10 (10 Hour discharge capacity)

483 = C5

425 = C3

304 = C1

__________________
En la casa del herrero, cuchillos de palo!
Reply
Reply to Forum Thread 5 comments