Zero Sequence Impedance Test in Transformer

11/10/2008 11:38 AM

Dear all

1)why zero sequence impedance test was conducted in transformer?

2)what information we will get from that test?

3) from test, how to calculate that zero sequence impedance ?

pl share ur views

cheers

gova

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: Zero Sequence Impedance Test in Transformer

11/10/2008 8:49 PM

Dear all,

1) 2)

Z0 (zero sequence impedance) Z1(positive sequence impedance) and Z2 (negative sequence impedance) are necessary to calculate unbalanced fault currents such as a line to earth fault.

Z0 is an impedance measured with a single phase voltage.

Z1 is an impedance measured with a 3 phase voltage source. Z1 is normally refereed as an impedance of a transformer.

Z2 is an impedance measured with a 3phase but opposite phase rotation such as (a-c-b not normal a-b-c).

In 3 phase transformer Z2 is same as Z1, so there is no need to test Z2 while Z0 is around 90% of Z1.

3)

Test voltage of rated frequency will be applied between the neutral of star and shorted 3 line terminals of a winding. All terminals including neutral of other windings will be shorted.

Adjust the test voltage so that the line current is the rated current of the transformer.

Z0 (Pu) = test voltage applied / rated line to neutral voltage.

or Z0 (ohm) = test voltage applied / measured line current.

= 3 x test voltage applied / measured neutral current.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Commentator
India - Member - New Member

Join Date: Nov 2008
Location: India
Posts: 72
#2
In reply to #1

Re: Zero Sequence Impedance Test in Transformer

11/11/2008 6:03 AM

Dear rakhesh and akhito

Thank u very much sir.

Now I am clear.

But in some sites,this test is not recomended.whether this test can cause any harm to transformer.

thanks and regards

gova

Register to Reply
Participant

Join Date: Feb 2009
Posts: 3
#3
In reply to #2

Re: Zero Sequence Impedance Test in Transformer

02/02/2009 9:00 AM

Hi Gova,

When we work with short-circuits problems can definately occur.

HOWEVER - this is a test in which the voltage applied at the primary must only be increased up to the stage where the secondary delivers full load. If this is done by a competent electrician, there will not be any problems.

Also make sure that the device applying the test voltage is able to deliver the necessary primary current for the test and that the cables on the short can handle the load. The transformer itself is designed for this load.

Register to Reply
Anonymous Poster
#4
In reply to #1

Re: Zero Sequence Impedance Test in Transformer

03/14/2009 6:25 AM

but how to convert ohms per phase to %Z0

Register to Reply Off Topic (Score 5)
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (1); Anonymous Poster (1); gova1467 (1); JohanGT (1)

Previous in Forum: source & sink input/output   Next in Forum: Fuse Naming T2AH250V, T4AL250V

Advertisement