how to select overload for 3 phase

11/11/2008 12:14 AM

how can i select an overload rating for 3 phase power ??? shall i calculate the equation like this form :

I= P/V*1.72*.85 assume power = 4 KW

I= 4000/380*1.72*0.85 = 7.2 A

So i have to select the overload depend on I=7.2A or i have to divide this current

by (3) 7.2/3= 2.4A

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: how to select overload for 3 phase

11/11/2008 5:34 AM
dear friend,

if you place the over load device in line, you have to select for 7.2 Amp, that is as per the line currents measured / calculated.

But if you place the over load device in phase windings, say in Star Delta Starters , then you need to select as per 7.2 / 1.732 Amp.= 4.3 Amp.

guest

Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#2
In reply to #1

Re: how to select overload for 3 phase

11/11/2008 5:40 AM

we NEVER place protective device(such us Thermal Overload Protection/TOR) inside motor winding.

We Always and MUST put the protection device after MCCB (for low voltage) whether the motor connected in delta or why. so in this case, current that flow through of TOR is Current Line ( I line) NOT I phase.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: how to select overload for 3 phase

11/11/2008 11:34 AM

If you are using a motor, and we must assume you are, then the only valid selection process is to read the motor nameplate current information. No formulae are necessary. If the motor nameplate says 7.2A, then you use an overload relay set for 7.2A. It is no more difficult than that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Engineering Fields - Piping Design Engineering - New Member Technical Fields - Architecture - New Member

Join Date: Apr 2006
Location: Bangalore India
Posts: 288
Good Answers: 3
#5
In reply to #3

Re: how to select overload for 3 phase

11/12/2008 12:40 AM

jraef you are right over load setting depends on Motor name plate information in this part of world the The Motor starters are supplied with built in over loads generally thermal over loads which are not that effective because by the time temperature for thermal tripping relay reaches the set temperature and trips the motor cable end termination on the motor would have caused the damage,hence i always set the overload trip slightly less than the name plate value to safeguard my self

CRM

__________________
Run silent run deep
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#7
In reply to #3

Re: how to select overload for 3 phase

11/12/2008 8:53 AM

Your overload must be set higher that the FLA in order to eliminate nuisance trips. In the US we reference the NEC section 430.32(2and thermal overloads need to be sized @ 170% for 9A or less, @ 156% for 9.1A- 20A, and 1450% @ greater than 20A

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#8
In reply to #3

Re: how to select overload for 3 phase

11/12/2008 8:56 AM

JRaef,

In the US we reference the NEC section 430.32(2) in order to eliminate nuisance trips that would result from sizing the overload at the FLA. 170% less than 9A, 156% 9.1A- 20A, and 140% greater than 20A

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Associate
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2007
Location: India
Posts: 42
Good Answers: 3
#12
In reply to #3

Re: how to select overload for 3 phase

11/12/2008 9:53 AM

Dear Sir,

We should not go by the name plate motor rated current in selecting over load relay of motor.We must select the overload relay current rating , based on the actual load of the motor supposed to deliver.

V.Ambarani

__________________
Best Regards
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: how to select overload for 3 phase

11/11/2008 11:46 AM

OL is always placed in the line.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#6

Re: how to select overload for 3 phase

11/12/2008 8:47 AM

You would use a thermal overload rated @ 12.24 A (reference NEC 430.32(2) 170% less than 9A. Reference NEC Table 430.52 for the shortcircuit and ground fault percentage ratings dependant upon the type of device utilized.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#9

Re: how to select overload for 3 phase

11/12/2008 9:25 AM

NEC 430.32(2) is for a Thermal Protector, which is integral with the motor. Selection of an Overload Device, which is integral with the motor starter, use NEC 430(1). That section states that the device shall trip or be rated at no more than the following percentages of nameplate:

125% for motors with a SF of 1.15 or greater

125% for motors with a marked temp rise 40 degrees C or less

115% for all others

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#10
In reply to #9

Re: how to select overload for 3 phase

11/12/2008 9:26 AM

Sorry, that should have been 430.32(1), not 430(1).

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
Anonymous Poster
#13
In reply to #10

Re: how to select overload for 3 phase

11/12/2008 4:47 PM

To finish that quote by Lincoln:"Bring me a list of all the ones that I can fool all of the time"

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#11
In reply to #9

Re: how to select overload for 3 phase

11/12/2008 9:36 AM

Good point, however, 430.31 is dependant upon the service factor of the motor.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Power-User

Join Date: Sep 2008
Location: Jakarta, Indonesia
Posts: 104
#18
In reply to #9

Re: how to select overload for 3 phase

04/27/2009 2:44 AM

============================================

125% for motors with a SF of 1.15 or greater

125% for motors with a marked temp rise 40 degrees C or less

115% for all others

=============================================

is this setting not depend on manufacture curve ?

is this setting already consider motor starting (that can reach 600%I FLA) ?

tx...

Register to Reply
Associate

Join Date: Jan 2007
Location: Raleigh, N.C.
Posts: 49
Good Answers: 1
#19
In reply to #18

Re: how to select overload for 3 phase

04/27/2009 6:48 AM

The setting is based on the NEC requirements and the max allowed under these conditions. Percentages are applied to manufacturers FLA, as indicated on ea motor.

Inrush should only be seen for fractions of a second and thus should have no bearing on the OLs.

__________________
"You can fool some of the people all of the time and you can even fool all the people some of the time, but you can never fool all the people all of the time." Abe Lincoln
Register to Reply
Anonymous Poster
#14

Re: how to select overload for 3 phase

11/12/2008 4:54 PM

Are you selecting for a single motor?

If so, determine the brand of motor starter you have, and consult the OL chart for that particular make, and use the motor load amps to determine.

If calculating main feeder calculation for a group of motors, use 125% of the largest motor, and 100% of all other motors in the group. Remember, fuses protect wiring, thernal overlaods protect the motor.

Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#15

Re: how to select overload for 3 phase

11/12/2008 11:27 PM

The motor you select for the job should always be capable of operating a less than its maximum kW ie if your mechanical load requires 3-4 kW then 4 kW is the minimum 5.5 may be a better choice. Use the name plate current rating as the MAXIMUM setting of your overload. If the overload trips at this then get a bigger motor. Operating a motor at more than its rated current will dramatically shorten its life. It is a good idea to check the operating current of the motor when it is operating under load and if lower than the name plate adjust the overload down to match. This will better protect the installation in case mechanical or other problems. Browse the schneider and AB sites for starters and overloads and ABB or Crompton for Motor info

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#16
In reply to #15

Re: how to select overload for 3 phase

11/13/2008 9:05 AM

TRhe overloads need to be sized greater than the FLA on the nameplate due to the fact that this rating is often exceeded due to inrush current at start-up.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply
Commentator
Engineering Fields - Power Engineering - Projects Engineer

Join Date: Aug 2008
Location: Tanzania- East Africa
Posts: 71
#17

Re: how to select overload for 3 phase

11/15/2008 4:24 AM

To get the best O/L protection measure the actual maximum current by clamp meter and set the O/L at 125% of the current reading.

The name plate indicates the max current and your motor will not necessrily run at max load.

__________________
A wise person will understand more from a Foolish question than what a Fool will understand from a Wise Answer
Register to Reply
Register to Reply 19 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); bfmickl (3); coconutpete (1); crm (1); elect-ok (2); JRaef (1); nesubra (1); noshorts (5); SAK (1); V.Ambarani. (1)

Previous in Forum: Trip Switches on 1ph winch trolley   Next in Forum: Load calculations

Advertisement